face26
2022-10-18 07:59:26
- #1
The heating load isn’t about the annual consumption but the value of heating energy you need at the design temperature. I don’t know that value now, but based on your other data and unless you live at the North Pole, the unit is obviously much too big. Your heating load will surely be below 6 kW, maybe even significantly lower. The problem isn’t so much that it has too much power "on top" (i.e., the 12 kW), but that it cannot modulate down. In other words, you only need 6 kW from my example if it’s -12 degrees for 3 days straight. The other 98% of the year you would get by with 2-3 kW. Yours can’t do that, so it will turn on and off more often. Presumably, this is why the installer gave you a nice big buffer. But if the damage is already done, that’s of course unfortunate.I have to honestly admit that I haven’t seen a concrete heating load calculation for our house yet, but according to the general contractor, the heating energy demand should be around 20kWh/sqm p.a. Roughly estimated, that’s about 4,700kWh p.a. I already asked him whether the ALM 4-12 isn't a bit "over the top." You can guess the answer. To my shame, I have to admit that I didn’t read deeply enough into the topic in time. Meanwhile, the heat pump is ordered and on its way. There’s not much I can do about it now. :-/ In hindsight, I should have taken the smaller unit, the ALM 2-8.