TmMike_2
2022-04-14 11:14:34
- #1
Yes and no, the DIN4701 was valid until 2003, after which it became invalid. Simplified procedures are still based on it.
Since then, the heating load has been correctly calculated according to DIN EN 12831.
You probably just found some very old performance specifications.
The hydraulic balancing is not legally required. However, it is a prerequisite for funding.
Apart from that, a heating system without hydraulic balancing doesn't make sense. For safety, the hydraulic balancing should be explicitly included - because, as always, you only get what has been agreed upon in writing.
Hydraulic balancing should actually be unnecessary in new buildings.
Give the heating engineer the energy calculation of your house.
He can then determine the hydraulic balancing for each room based on the room heat demand, the pipe length, and the calculated pipe friction losses.
Then the actuators hardly remain necessary, and the heat pump operates at maximum efficiency.
In my case, the engineering office of the heat pump manufacturer calculated these values for the heating engineer. That should actually be possible with a heat pump costing 7-10k.