chand1986
2023-02-21 12:49:24
- #1
And how do you come up with the 500 cubic meters? I’d have to run it full blast for a whole hour. In reality, full blast runs for a maximum of 10 minutes during a frying process, and even then only for red meat or the famous herrings. With a short pre-run and a somewhat longer post-run. And you have a 20°C difference during cooking times at what percentage of the heating season? Let me be very(!) generous and assume 0.5 kWh heat loss per cooking process during the heating season. In reality, it will be even less, arguments see above. Cooking daily on 120 days per year then makes 60 kWh. I recover half of that alone as waste heat from the stove. The rest is produced in the new building with an annual performance factor of 3. That is, sorry for the expression, a drop in the ocean. People just make good money on recirculation systems.There is a difference between exhaust air without heat recovery and ventilation with heat recovery. In one, the heat stays inside and the moisture goes out, in the other, both go out. And now we can do some calculations. Heating 1 cubic meter of air by 1 degree requires 0.33 Wh. With a temperature difference of 20 degrees and 500 cubic meters of air exchange, 3.3 kWh of heat energy are lost through the exhaust hood. With a recirculation hood and ventilation with 80-90% heat recovery, it's only a fraction of that. In grandma’s uninsulated house from 1965 with 250 kWh/sqm, that doesn’t matter. In new buildings, it does not.