Yes, but: what is it good for?
It is the lesser evil. Officially, it is about grid stability and avoiding high peaks, but in my opinion, it is simply a result of lobbying.
Since 2012, the Renewable Energy Act requires that even small systems <30 kWp must be grid-service controllable. However, the ripple control receiver (RSE) usually used for this and the additional effort in the household installation greatly impair the economic viability of such small systems. Therefore, there is the alternative to limit the feed-in fixed at 70% of the generator capacity at the inverter ("70% hard" in photovoltaic jargon). That means 30% of the generator capacity is flat-out thrown away. Alternatively, there is the possibility to implement "70% soft." In this case, the current household consumption is measured additionally, so that the photovoltaic system feeds in the "hard" 70% generator capacity plus the current consumption of its own household. Less production is wasted then.
research86 rightly noted that with an east/west system, the 70% soft regulation is usually not necessary at all, since this type of system does not deliver high peak power anyway. The south system has a strong peak at noon, whereas the east/west system shows a flatter power curve over the day. flatten the curve If you orient a 10 kWp system to the south, as a simplified example, 10 kW can come from the roof at noon; with "70% hard" only 7 kW would be allowed to feed in. With east/west, you also have a 10 kWp system, but 5 kWp are oriented east and 5 kWp west. Thus, you never reach the allowable 7 kW feed-in power.