They are here too.
Basically, I would request the heating load calculation "for the documents." 35°C is really not too ambitious as a target value.
It will work, and you can’t always optimize everything during construction. That makes you old.
13 heating circuits for 144 sqm? I find that too few. We have 13 heating circuits for 90 sqm. Note the pipe diameter from the heat pump to the heating circuit distributor. Do not let any bottlenecks be installed here, use sufficient pipe diameter. According to some experts, lowering the supply temperature (VLT) by 1 degree means an efficiency increase of 2.5%. Thus, reducing the supply temperature from 35 degrees to 31 degrees means an efficiency increase of 10%. Even an 8% improvement would already be a good result. You had written that the screed will be installed soon. So beforehand, the underfloor heating must be installed. For this, the heating engineer needs the heating load calculation for laying the underfloor heating! Keep in mind that mistakes in the design of the underfloor heating remain in the house forever. You can always change your heat pump, but not your underfloor heating. For the design, we chose 22 degrees in the bathroom and 21 degrees in the other rooms. Everywhere a laying distance of 11 cm, bathroom 5.5 cm also under shower and bathtub. How much power does your heat pump deliver? From my point of view (subject to a correct calculation), 5, max 6 kW should be sufficient.