Air-water heat pump current consumption and data

  • Erstellt am 2020-09-29 11:06:43

Daniel-Sp

2021-02-09 12:16:59
  • #1
You should balance the volume flows against each other and have equal volume flow in both circuits. Only in this way can you prevent turbulence in the buffer. Because that costs efficiency and thus a higher heating curve will be required. However, I do not know your buffer and cannot say whether turbulence-free flow is possible at all. There are buffers that have baffle plates installed at the inlet. If you have such a model, turbulence-free flow will be difficult. The differential is then only of secondary interest. The mixer must, of course, not mix. Depending on the power of the heat pump, I have a differential of 2-4.5K during the heating cycle and it gets warm.
 

Alessandro

2021-02-09 12:56:39
  • #2
yes, I understand that.
But if the differential temperature in the underfloor heating is lower than that of the heat pump and the flow rate of the secondary pump is fixed while the heat pump is modulating, the flow rate of the heat pump will always be lower than that of the underfloor heating.
Optimal would be the exact opposite: flow rate of the heat pump slightly higher (100-200l/min) than that in the underfloor heating.

If the secondary pump runs at level 1 with constant pressure, I have heat pump flow = underfloor heating flow without losses and an exact differential temperature of 5K in the underfloor heating!
However, it then only has 900l/min, 1.8m and approx. 12W



Is it possible that a medium temperature eventually establishes itself in the buffer when all the water is completely mixed?
 

Alessandro

2021-02-09 13:07:36
  • #3
or should I set the spread of the heat pump to 3K as well?
 

Daniel-Sp

2021-02-09 13:16:33
  • #4
Doesn't the heat pump regulate the spread independently?
 

face26

2021-02-09 13:17:22
  • #5
I'm not a pro, I haven't understood your setUp yet. How big is the buffer? Is it a pure heating buffer? So hot water separate? To what temperature do you heat the buffer?
 

Daniel-Sp

2021-02-09 13:20:36
  • #6
I already told you that in the other thread. With a modulating heat pump this mixer/buffer construction is really bad precisely because of the modulating flow volume in the primary circuit and fixed flow volume in the secondary circuit.
 

Similar topics
20.10.2016Water-bearing fireplace stove floor heating, heat pump, photovoltaic, new construction?28
19.09.2023Cooling via underfloor heating with brine heat pump45
19.05.2021Experiences with brine heat pump491
25.11.2015Offer air-water heat pump including underfloor heating, ok?19
18.04.2016Heating circuits/thermostats for living/dining/kitchen with underfloor heating/heat pump35
30.12.2017Heating system new construction (heat pump + stove + solar)35
06.06.2019Cooling in summer with air-to-water heat pump, underfloor heating and/or ventilation system?29
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
12.11.2021Central room temperature controller for ERR underfloor heating76
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
24.08.2021Cooling with heat pump via underfloor heating?117
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
25.05.2022Air-to-water heat pump + underfloor heating + controlled residential ventilation with heat recovery - individually room differently temperature controllable?10
02.02.2023Individual room control with air-water heat pump and underfloor heating20
26.06.2023Heat pump, water storage tank, instantaneous water heater, wfK, underfloor heating, heating and cooling12
24.11.2023Heat pump: buffer tank, capacity and modulation46

Oben