How have you set your domestic hot water circulation? Something like that can also be a real energy guzzler.
As winter is approaching again, I am trying out a few things. I have a 100L parallel storage tank, a mixer, and an HTHK. This is now the second heating season coming up for me.
Since I keep wondering why manufacturers specify such a hydraulics setup to minimize cycling or increase runtime, I have reset all settings and the hydraulics back to "factory settings."
Specifically, that means:
Heating curve of the underfloor heating: 18°C = 22°C return flow 0°C = 27°C return flow -15°C = 30°C return flow
The heat pump heating curve 5K above that of the underfloor heating: 18°C = 27°C return flow 0°C = 32°C return flow -15°C = 35°C return flow
The mixer mixes! UWP set to proportional pressure, ERR activated. Compressor power minimized.
The last two days with AT somewhere between 7-11°C, I have cycles of about 3 hours even though the underfloor heating flow through the ERR is between 1200 and 600L/min.
Last year, at such ATs, cycles were about 25 minutes!