By compiling all the data, I have probably found the problem. The minimum performance of the heat pump is 1200l/h, I knew that.
Even though the heat pump ran well over the last 7 days, this value was clearly undershot at 1041l/h. See screenshot.
I have now set it like this. See
1st screenshot Excel.
2nd screenshot was 30 minutes ago
3rd screenshot was just after adjusting the new flow rates.
Offset differential is now gone. I will take care of the temperature in the individual rooms and the radiators. Hopefully, the heat pump runs smoothly from now on.
Fingers crossed. Let's see, we will know after the next heating cycle. I'll get back to you and sorry for nagging