Air-water heat pump current consumption and data

  • Erstellt am 2020-09-29 11:06:43

Zaba12

2021-01-09 11:40:14
  • #1
By compiling all the data, I have probably found the problem. The minimum performance of the heat pump is 1200l/h, I knew that.

Even though the heat pump ran well over the last 7 days, this value was clearly undershot at 1041l/h. See screenshot.

I have now set it like this. See
1st screenshot Excel.
2nd screenshot was 30 minutes ago
3rd screenshot was just after adjusting the new flow rates.

Offset differential is now gone. I will take care of the temperature in the individual rooms and the radiators. Hopefully, the heat pump runs smoothly from now on.

Fingers crossed. Let's see, we will know after the next heating cycle. I'll get back to you and sorry for nagging
 

Daniel-Sp

2021-01-09 11:45:01
  • #2
The minimum flow rate is required to remove the heat from the heat pump. If the flow rate is too low, the heat "backs up," the supply temperature rises until you get an error message with a protective shutdown. I had quietly suspected this and asked about the total flow rate.
 

OWLer

2021-01-09 11:46:30
  • #3
What exactly did you change before the problem occurred? During the course of the week, it ran well and economically.
 

Zaba12

2021-01-09 11:53:47
  • #4
Actually nothing except, as I said, on 01.01. I turned off the basement, after that it ran well or really smoothly with low consumption and a comfortable indoor temperature, apart from the relatively high spread (which has always been relatively high) and which apparently escalated until yesterday. So up to page 13. :cool:
 

Zaba12

2021-01-09 13:50:21
  • #5
Status update: Looks good. Quiet for 2:41 hours, return temperature is slowly and steadily decreasing. Spread 0.2K, return 27.8 degrees.

I will upload a csv and dta later.
 

lin0r87

2021-01-09 15:47:35
  • #6
hey everyone,
I read through everything and I'm a bit confused...
We have a Novelan LAD9 system with a photovoltaic and only one meter.

Not much is running on the equipment.
- Controlled residential ventilation
- Bus system
- usual consumers like fridge etc.

I noted the value from yesterday and checked the meter today.
I came to a total consumption of about 30kWh/day. Electricity
I wonder if our device might be set incorrectly...?

We have the same menu on the device as
 

Similar topics
10.12.2009Subsidies for KFW55 and Sole/Water Heat Pump15
06.01.2012Geothermal vs. Air-to-Water Heat Pump12
19.05.2021Experiences with brine heat pump491
14.10.2017Heat pump flow temperature experiences?13
30.12.2017Heating system new construction (heat pump + stove + solar)35
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
19.03.2021Combine air-water heat pump with water-carrying wood stove57
16.04.2020Recommendation for digital room thermostat for air-to-water heat pump16
14.10.2022Air-to-water heat pump sizing in new construction311
14.12.2020Ice formation brine pipe heat pump78
20.11.2020Air-water heat pump flow temperatures34
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
25.06.2021Dimplex SI8TU ground source heat pump - strange behavior15
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16
24.11.2023Heat pump: buffer tank, capacity and modulation46
11.11.2023Heat pump in the transition period34
13.02.2024Heat pump is not compatible with a water-bearing fireplace144

Oben