With my settings, overloading the buffer by 5K, active mixer (heating curve 5K below heating curve for buffer charging), I come to about 700kWh for November (200 sqm, designed according to energy saving regulations). Temperatures are 22°C, bathroom 23.5°C. Average runtimes about 3 hours with active ERR.
Through the mixer I found out (because I can determine the flow temperature exactly here) which heating curve the house needs and that is exactly 33°C at NAT.
Heating curves were (return flow):
Heat pump:
27°C at 18°
32°C at 0°
35°C at -15°
Mixer:
22°C at 18°
27°C at 0°
30°C at -15°
Hysteresis (heat pump):
5K at 18°
4K at -15°
Since the buffer construction (or the buffer itself) causes a dT from heat pump flow to underfloor heating flow of about 2K, I have now tried to lower the heat pump’s heating curve by 3K and reduce the hysteresis to 2K with the ERR open (here the heat pump flow rate = underfloor heating flow rate).
In the ground floor the temperatures are exactly as I want them.
In the bathroom and the guest room, however, they have each dropped to 21°C.
I don’t understand why? Do I have a thinking error?