Air-water heat pump current consumption and data

  • Erstellt am 2020-09-29 11:06:43

Zaba12

2021-01-21 19:19:23
  • #1
The pump after-run time is set to 5 minutes.

Measured at the sleeve where the return and flow sensors are located.

In my opinion, this should not happen in standby, that's how I understood it. Or not that high. And this is currently low. I have had 8K between flow and return in standby before.
 

T_im_Norden

2021-01-21 19:32:09
  • #2
Is the difference also present at the HKV?
 

Zaba12

2021-01-21 19:48:33
  • #3
Return flow and supply flow in the upper floor HKV 24.6 degrees without deviation. At the heat pump, the return flow is currently 22.5 degrees and the supply flow 24.2 degrees
 

T_im_Norden

2021-01-21 20:04:22
  • #4
And at the lower HKV?
 

Zaba12

2021-01-21 20:06:40
  • #5
Here, take a look, the handwritten notes are the measured return temperatures at the HKV on the ground floor from January 9th at 11 a.m., where the temperature spread really escalated. At the HKV, the return temperatures are somewhere around 28-31 degrees. The sensor of the heat pump shows something around 25 degrees.

 

Zaba12

2021-01-21 20:10:03
  • #6
24.3 return and supply
 

Similar topics
28.08.2013New single-family house, gas or heat pump, target KfW5529
19.05.2021Experiences with brine heat pump491
14.10.2017Heat pump flow temperature experiences?13
30.12.2017Heating system new construction (heat pump + stove + solar)35
17.04.2018Heat pump domestic water storage tank - What size is recommended?12
22.11.2019Feedback on heat pump / offer requested!46
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
20.12.2019Difference in purchase cost between gas pump or heat pump74
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
19.03.2021Combine air-water heat pump with water-carrying wood stove57
14.10.2022Air-to-water heat pump sizing in new construction311
14.12.2020Ice formation brine pipe heat pump78
20.11.2020Air-water heat pump flow temperatures34
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
14.06.2021Separate meter and electricity tariff for air-to-water heat pump sensible?103
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
11.11.2023Heat pump in the transition period34
13.02.2024Heat pump is not compatible with a water-bearing fireplace144
02.12.2024Correct adjustment of the heat pump in connection with the wood stove12

Oben