We have 2 times 70 meters drilling depth and 10 m supply line to the house.
The extraction capacity was, I believe, about 43 W/m (still in the box - was definitely better than the assumed 39 kW from the neighborhood according to LBeg).
It was grouted with Thermocem Basic (unfortunately - we didn’t know about that).
190 sqm, 5.3 kW Flexothem Exclusive, heating load is 5.5 kW (U-value, myself) - 6.3 kW (Vaillant); where I trust the U-value more than Vaillant, as Vaillant did not really consider the heat recovery of the ventilation (0.5 kW with U-value; 1.5 kW with Vaillant for the required heat output to compensate for the minimum air exchange rate).
I’m currently checking live again:
Energy integral at: -100 min (start -120 min)
Set flow temperature at: 27.5 °C
Flow temperature is at: 29.5 °C
Brine inlet: 3.4 °C
Brine outlet: 1.6 °C
Heating curve at 0.1 and desired temperature at 23 °C (it’s just the offset)