4000 is more like the 10-year goal, although it still depends on whether it is a modulating pump or not.
UPS, ok, well great. What causes that? Why this frequency?4000 is more like the 10-year target, depending on whether it is a modulating pump or not.
The Energy Saving Ordinance requires ERR for heated rooms. Since heat pump manufacturers assume that they are also used (and thus several heating circuits are closed), but the heat pump needs a minimum flow rate, measures such as bypass valves and buffer tanks are required in the installation diagrams. The heating engineer follows these hydraulics schemes approved by the manufacturer in order to always be able to say in case of problems that it was built as required by the manufacturer.
What happens: Due to the ERR, heating circuits are closed, the minimum flow rate is undershot and the pressure rises, the bypass valve opens and warm flow flows directly into the buffer in the return line. The buffer can only store a minimal amount of heat, so the return temperature rises within a short time. Your heat pump is return controlled. After a short time, the setpoint return temperature plus hysteresis is reached and the compressor switches off. In your case on average after 14 minutes. The compressor stops, the heating water circulation pump continues to run as intended, the flow temperature drops and so does the return temperature. Because the screed in the open circuits is still cold (cool), the measured return temperature falls below the lower hysteresis band after a short time and the compressor starts and the game with the short circuit via the bypass valve starts all over again. If your heat pump did not produce hot water, the average compressor running times would probably be even shorter. To get heat into the rooms in the short running times, the heating curve is set much too high. But that only worsens the problem.
I assume that your heating engineer adheres to the installation instructions from the manufacturer and does not uninstall the ERR on Monday (or set it to max) and fully close the bypass valve. You will have to deal with your heating system yourself.
You don’t have a bad heat pump, it is just operated incorrectly.
We have lived in our house since August and have just "managed" 210 compressor starts. Also a Novelan heat pump...
Regards, Daniel
Hi,
The password to change the WW hysteresis is 9445. If it is too cold, raise the heating curve to 30/22/0.
Since you write that the ERR is set to 22-23 degrees, I assume that not all ERR are set to maximum. What total flow do your flow meters on the heating circuit distributor show? And the all-important question is: Is the bypass valve completely closed? I suspect not.
You should use today to read the operating manual of the heat pump controller, also the one for the professional technician (you can find it on the homepage). Tomorrow, have the bypass valve shown to you, as well as an explanation of how to operate the top meters in the heating circuit distributor (completely open, ask about additional flow restrictors in the supply and return).
Which model was installed?
Yes, the control system is complicated. And most only notice the problems after a few years when the heat pump breaks down. The technician acts according to the manufacturer's instructions.
You have to take care of it yourself.
If the heat pump no longer cycles and the heating curve roughly matches, then the hydraulic balancing comes, but not via the ERRs but via the top meters. If everything is correct, you will no longer have to touch the heating.
Important are also the lengths of the individual heating circuits!