If yes, then here you go. Weak nerves please skip this part.
[Masonry:]
- The masonry top surfaces (gable and dormers) were neither capped nor covered and not insulated. Cold air inflow occurs.
- In the dormers in the attic, there are loose bricks in the masonry, the masonry is pieced together and must be dismantled
- There are gaps up to 12 cm between the verge and the masonry on all 4 gables, these must be closed with masonry
- The single-leaf exterior masonry shows significant defects concerning the substrate for the facade plaster. To avoid cracks, the implementation of a decoupled plaster system is necessary (ultralight plaster for decoupling and full-surface fabric reinforcement, minimum plaster thickness of base coat 15 mm required, then approx. 5 mm fabric reinforcement and top coat, total thickness 20 to 25 mm). The minimum plaster thickness was not observed on the currently applied plaster surfaces. The facade surface is uneven.
- The holes and joints were not grouted as required.
- The rafters were not filled with masonry and were only clad with insulation. The connections to the rafters were executed without a movement joint. Necessary measures: - contractually compliant masonry filling
- Styrofoam and construction foam were used on the dormers on the upper floor; these must be removed and replaced with masonry
- The interior walls on the upper floor are incompletely built in the slopes
[Roof:]
- Despite contractual agreement, the under-roof membrane was not replaced after 7 months of weather exposure
- Underlay membrane not professionally installed and incomplete
- Tiles partially damaged/chipped
- Valleys crooked/skewed
- Bird protection loose and incomplete
- Lead tape under all windows loose
- Gutter hangs too high
- The roof windows are set too high and additionally at different heights
- Dormer insulation incomplete
- On the left dormer, the roof tiles do not reach the masonry
- Right dormer not completed
- The verge boards were not painted
- Verge boards on the rafters incomplete
[Attic:]
- Complete renewal of vapor barrier and drywall
- Consideration of apartment separation
- Renewal of electrical system
- Relocation of door openings
[Heating/Plumbing:]
- Completion of floor heating in basement – connection to both heating circuits
- The drainage pipe of the left apartment is not connected
- Installation must be renewed as the slope is in the wrong direction
- In all 4 bathrooms, the minimum screed thickness under the showers is not met
- Under the bathtubs, the minimum screed thickness is not met
→ Removal of screed in all 4 bathrooms, reduction of insulation under screed; removal of floor heating under the bathtubs, new screed installation
[Electrical:]
- Protruding sockets to be sanded down
- Renewal in the attic
- Garden power boxes missing
[Windows:]
- Lockable window handles and hinge covers missing
- Both terrace doors must be replaced (too short)
- Dormer window in the right apartment damaged
- Bathroom windows are not frosted
- Mouse guards missing on basement windows
[Window sills:]
- Due to the missing grouting of the external joints (see contract), insulating plaster must now be used
- Since this is thicker and the external window sills were already dimensioned too narrowly (see expert report), these must be replaced including upper drainage grooves
- Interior window sills incomplete
- Basement windows missing interior window sills
[Interior plaster:]
- The full-surface reinforcement required by contract is not present, the plaster shows cracks and must be renewed
- The surface quality does not correspond to quality level Q3 in parts
- The concrete walls in the basement are not plastered
- No cove cut / separation cut was made at the connection to the concrete ceilings. The plaster is already breaking out in places. Necessary measures: - Production of separation cuts - Installation of the contractually agreed Magic Corner profiles
- The masonry behind the knee wall cladding and at the level of the wooden beams was not plastered or filled. Wind tightness is not guaranteed.
- The areas plastered by Mr. Langner must be chipped off and replastered because 1. no primer was applied and 2. overlapping sack material stored outdoors at -20 degrees and not dry was used
- Window reveals to be reopened, reinforcement to be worked in, Vediplatte to be set over the roller shutter box, close
[Putty work:]
- The ceilings and walls in the upper floor, puttied by the company Langner, were consistently not primed. Cavities are present in places, which chip off.
- The putty layer must be removed, the plaster inspected and if necessary removed as the required reinforcement is missing.
[Basement:]
- Ceiling penetrations to the basement are not sealed (fire resistant)
- The already puttied ceilings and walls were not primed
- Cladding of heating pipes missing
- Closure of ceiling and wall joints
- Cable ducts still open
[Miscellaneous:]
- Laying of empty conduit for photovoltaic system missing
- Defect correction of the shell construction not completed: plinth preparation