Underfloor heating air-water heat pump. House too warm when the sun shines

  • Erstellt am 2019-12-04 14:18:21

Daniel-Sp

2019-12-21 14:06:54
  • #1
The question is whether you get more flow through the underfloor heating if you slowly (step by step) close the bypass valve? You still have 26 compressor starts in 48h. I have 3 per day.
 

chewbacca123

2019-12-21 15:53:29
  • #2
Can nothing happen if you gradually close the valve? So can nothing break if pressure builds up that is not released?
 

Daniel-Sp

2019-12-21 17:00:08
  • #3
Then the heat pump gives an error message and shuts off. You can then reopen the bypass valve and reset the error. Therefore, close it step by step when the pump is currently heating, you just have to adjust, or briefly raise the heating curve to initiate a heating process.
 

Daniel-Sp

2019-12-21 17:06:34
  • #4

This is because hot water reaches the return flow too quickly. However, this does not happen with water that flows through the circuits of the underfloor heating, but with water that flows past the heating circuits. So in your case, via the bypass valve. Regardless of how powerful the heat pump is.
 

Daniel-Sp

2019-12-21 20:07:57
  • #5

For the estimation, you need Ht, envelope surface area, heated gross volume, desired temperatures, standard outside temperature, number of occupants.
You can find these, for example, in the KFW certificate.
This will get you a good estimation.
 

chewbacca123

2019-12-21 20:27:15
  • #6
We did not build a KfW house‍
 

Similar topics
13.06.2012Underfloor heating and mechanical ventilation with heat recovery (MVHR), replacement of ordinary radiators23
09.12.2012Climate blanket vs. underfloor heating13
12.02.2013Heating single-family house, underfloor heating conversion, insulation, gas boiler defective19
24.07.2013Additional costs due to underfloor heating11
20.10.2016Water-bearing fireplace stove floor heating, heat pump, photovoltaic, new construction?28
19.09.2023Cooling via underfloor heating with brine heat pump45
25.11.2015Offer air-water heat pump including underfloor heating, ok?19
18.04.2016Heating circuits/thermostats for living/dining/kitchen with underfloor heating/heat pump35
06.06.2019Cooling in summer with air-to-water heat pump, underfloor heating and/or ventilation system?29
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
24.08.2021Cooling with heat pump via underfloor heating?117
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
25.05.2022Air-to-water heat pump + underfloor heating + controlled residential ventilation with heat recovery - individually room differently temperature controllable?10
02.02.2023Individual room control with air-water heat pump and underfloor heating20
26.06.2023Heat pump, water storage tank, instantaneous water heater, wfK, underfloor heating, heating and cooling12
22.02.2024Heat pumps require a lot of energy and make noise73
05.03.2024Is a buffer tank useful in a heat pump?72

Oben