I correct myself, the data should be included in the documents/calculations from your energy consultant.
It makes sense to do a room-by-room heating load calculation and design the underfloor heating based on that with the appropriate supply-return temperature. Then select the heat pump accordingly. Unfortunately, this is rarely done. Usually, a heating load per square meter for the entire house is assumed and applied to all rooms, regardless of how many exterior walls a room has. When the underfloor heating is then designed based on this, it doesn’t match in some rooms (mostly bathrooms). The heat pump is then selected by guesswork, often hopelessly oversized...
In the documents from our energy consultant, there was no room-by-room heating load calculation. The company commissioned by the heating installer also did not perform a room-by-room heating load calculation but assumed a flat heating demand per square meter. So, that meant doing it yourself or commissioning it externally.