Underfloor heating air-water heat pump. House too warm when the sun shines

  • Erstellt am 2019-12-04 14:18:21

chewbacca123

2020-01-05 12:14:42
  • #1
For everyone who has been following the topic here, a final note about our heating: With the great help of all of you, especially Daniel, we have managed to reduce the impulses of the compressor from 100 per day to about five per day at our home. The heat pump now runs much more efficiently, really great. By closing the ÜV, our heating also no longer looks like a heart attack. The opendta program is really excellent; someone did a great job, and I now check the development daily, but it is really satisfactory. I will definitely continue to address the fact that the bathroom still does not get satisfactorily warm. 20.5 degrees is too cold, and that at 3l/min volume, the highest level. The new issue now is our water circulation; it does not circulate as I set it by timing. But we will somehow solve that too. Many thanks again to everyone who was and is so actively involved here – you are great!!!
 

chewbacca123

2020-01-05 17:10:06
  • #2
I can measure the return flow in our system, a few days ago during the heating cycle the supply was 34.5 and the return was 28.2. It is set to 3 l/min, the highest volume you can set. But it simply does not get warmer than 20.8° when the outside temperature is around 0°. So annoying. For comparison, the hallway is set to a volume of 0.25 l/min and it is 23° in the hallway every day.. Children's room 0.5 l/min and 22 degrees.
 

tomtom79

2020-01-05 17:39:49
  • #3

Unfortunately, it was planned incorrectly; many more pipes should have been installed, e.g., with a 5cm spacing. Or an electric auxiliary heater was planned in advance like in our case. I wish I had dealt with that more back then... I left out the auxiliary heater because the door is always open anyway.


I don’t know, I’m still reading and learning myself.
 

chewbacca123

2020-01-05 18:13:58
  • #4
Yes, more preparation should have been done in advance, but we really had zero knowledge about the subject. It really annoys me now... Especially that the expert apparently had no clue either... grrrrr
 

Daniel-Sp

2020-01-05 18:33:59
  • #5

Return-controlled seems more elegant to me, as the heating system measures based on the return temperature whether the screed has reached its temperature. Otherwise, you need some kind of room sensor that measures the room temperature and reports it to the heating system. That means additional wiring. Do you have something like that?
 

Musketier

2020-01-05 20:40:21
  • #6
I can't tell you exactly according to which system the pump for the underfloor heating starts. I would have to check that myself again. The heat pump itself is supply-controlled and heats a combination tank for us. The system is from Lüumel with a DV heat pump from Sofath.
 

Similar topics
19.05.2021Experiences with brine heat pump491
21.01.2016Is the heating oversized?44
14.10.2017Heat pump flow temperature experiences?13
14.09.2018Heating (Heat Pump) Incorrect, heat output too high?14
19.03.2021Combine air-water heat pump with water-carrying wood stove57
16.04.2020Recommendation for digital room thermostat for air-to-water heat pump16
14.12.2020Ice formation brine pipe heat pump78
04.01.2022Air-water heat pump current consumption and data1439
20.11.2020Air-water heat pump flow temperatures34
07.06.2021Installation of heat pump/heating - before or after screed16
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
05.07.2022Renew old heating with heat pump or gas boiler and domestic hot water heat pump58
09.10.2022Heating, something is wrong here. Hallway always 22°..27
15.12.2022Electricity consumption heat pump experiences?22
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16
07.10.2023How to plan heating with a heat pump in new construction?14
11.11.2023Heat pump in the transition period34
13.02.2024Heat pump is not compatible with a water-bearing fireplace144

Oben