Underfloor heating air-water heat pump. House too warm when the sun shines

  • Erstellt am 2019-12-04 14:18:21

Daniel-Sp

2020-01-05 20:48:43
  • #1
I am not familiar with DV-WP. Does such a system need a combination tank?
 

Musketier

2020-01-05 20:59:46
  • #2


No idea if a storage tank is mandatory for a DV.

Lüumel developed a storage tank where the domestic hot water is heated in flow through the heating water. So there is no domestic hot water storage tank. It's called a stratified storage tank with different temperatures at the top than at the bottom.
 

tomtom79

2020-01-09 15:07:05
  • #3
Buy yourself an IR thermometer for 15 euros, I still found errors in the hydraulic balancing in my system. Some heating circuits throttled the heat pumps too early because the return flow increased too early.

And one of the 3 heating circuits in one room was throttled too much, which makes no sense since the others are heating more.
In the hallway exactly the other way around.

Etc.

Now wait another 24 hours and see if it made any difference.
 

M4rvin

2020-01-09 22:54:54
  • #4
Does every heat pump regulate when the return flow is too warm?

A technician regarding the hydraulic balancing is coming to me soon, what should I pay attention to? So what definitely should be done?
 

tomtom79

2020-01-10 00:01:13
  • #5
He will set the calculated values for the flow rate. Whether these are actually acceptable in practice, you will only find out when you live there.
 

Daniel-Sp

2020-01-10 00:29:03
  • #6
Have a detailed documentation of the underfloor heating handed over to you. Laying distances, actually installed circuit lengths (not just what was calculated beforehand), pipe diameters (also of the pipes to the hydraulic balancing valve), hydraulic diagram, installed components. Instruction in the functionality/operation of the flow measuring tubes, ask about any additional flow restrictors in the supply and return. Additional bypass valves and their operation. These are pieces of information you would otherwise be chasing in vain by phone. Ask Chewbacca123... You will have to do the thermal balancing yourself in the next proper winter anyway.
 

Similar topics
25.01.2016Hot water only with heat pump?10
13.07.2016Photovoltaic storage - experiences? Tips?17
10.10.2017New photovoltaic system with storage in single-family home - experiences39
17.05.2017Photovoltaics initially without storage54
16.03.2017Long waiting time until hot water arrives17
05.03.2018Photovoltaic planning - possible retrofitting of battery storage13
31.07.2018Storage heats collector10
13.07.2019It takes a long time for hot water to come27
20.11.2019A circulation pump for hot water. Yes or No?41
07.05.2020Collaboration of air-water heat pump, photovoltaic system, and storage38
05.05.2020Photovoltaic system + storage with or without cloud tariff13
08.05.2020Heat pump + photovoltaic system with or without storage11
27.09.2020Oil heating system approximately 25 years old, storage defective15
13.08.2020Is energy storage also unprofitable for electric cars? Costs of wallbox + storage79
20.08.2021Hot water 60 degrees due to Legionella risk12
11.10.2021Actuators are open but no flow13
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
20.09.2023Convert hot water from solar thermal system to photovoltaic system?12
17.10.2023Evaluation of Photovoltaic System Offer with Storage78

Oben