Underfloor heating air-water heat pump. House too warm when the sun shines

  • Erstellt am 2019-12-04 14:18:21

chewbacca123

2019-12-27 19:57:35
  • #1

Great, that really makes me happy. Then I will adjust the heating curve down later so that we don’t end up with a sauna in the house. I’m already looking forward to how much energy we can save.
THANK YOU
I will report further, tomorrow I will close the bypass valve from five to 5.5
 

chewbacca123

2019-12-27 20:02:17
  • #2
27 is the flow temperature and 22 the room temperature (my installer said).
 

Daniel-Sp

2019-12-27 20:17:19
  • #3
No, 27-22-0 describes the heating curve. The heating system does not know at any time how warm it is in the rooms. 27 is the endpoint, i.e. the return flow temperature at -20°C, 22°C is the footpoint, i.e. 22 °C return flow temperature at 22°C outside temperature. On this curve, the heat pump adjusts the return flow temperature based on the measured outside temperature. If it is too warm or cold in the room, you have to adjust the heating curve... The 3rd number indicates the night setback, but usually makes little sense. You can experiment with it when everything is running smoothly. Oh yes, for me it hissed and bubbled briefly for one or two seconds when I had completely closed the overcurrent valve...
 

Daniel-Sp

2019-12-27 20:21:02
  • #4
No idea, in any case it works with Novelan and Alpha Innotec heat pumps. Thanks to a diligent programmer, you can visualize the data with a free tool.
 

M4rvin

2019-12-27 20:27:04
  • #5
Ok, I can't set something like that at all... I always thought the control regulates that automatically based on the outside temperature.
 

boxandroof

2019-12-27 20:58:44
  • #6
That varies depending on the manufacturer. Ours, for example, is controlled via the flow temperature. For native visualization, I would need an additional module. Due to photovoltaic and the temperature fluctuations throughout the day, I run a night setback and day boost. But that is a bit more difficult to adjust; everything else should be right beforehand.
 

Similar topics
19.05.2021Experiences with brine heat pump491
15.01.2018Is nighttime lowering of the heat pump sensible?13
05.02.2020LW Heat Pump Alpha Innotec LWDV with 12KW26
04.01.2022Air-water heat pump current consumption and data1439
09.11.2020Technical comparison of air-to-water heat pump25
06.03.2023Alpha Innotec heat pump failure23
22.09.2022Is night setback sensible? - Experiences?20
25.02.2023Is my heat pump from alpha innotec good?10

Oben