Underfloor heating air-water heat pump. House too warm when the sun shines

  • Erstellt am 2019-12-04 14:18:21

Bookstar

2021-01-12 09:41:59
  • #1
So, there was a fault 760 defrost again last night. The whole house is also getting cooler, about 1 degree lost.

Today I switched the efficiency pump from automatic to manual. Now it runs at 1500 l/h instead of 800 l/h. This also doubles the flow rate in the bathroom.

I'm curious to see what happens. Maybe the whole system will completely fall apart now.

I read in another forum about voltage numbers of the pump: 10 volts nominal and 3 volts eff. I don't see any of that with me, no settings possible.

It would be great if one of you could look into the menu to see what options are available under efficiency pump settings or if you find this voltage setting anywhere?
 

Alessandro

2021-01-12 09:46:30
  • #2
which settings can you choose on the pump? Shouldn't it directly "modulate along" with the heat pump?
 

Bookstar

2021-01-12 09:51:14
  • #3
I can choose automatic, then it modulates along. But in my opinion that doesn't work for me, because the flow rates are too low. That's why it's now set to manual with 100% max and 40% min.
 

halmi

2021-01-12 09:55:00
  • #4
have you reduced many circles? What software version does your machine have?
 

Bookstar

2021-01-12 10:06:08
  • #5

All circuits are open. The software version is the latest, installed two weeks ago, I am uploading a csv here.




















































































































































































































































































































































































































































01/12/2021 10:12
System status:
Heat pump type LWA 12
Heat pump type HDT_9
Software version V3.85.6 (r6445)
Bivalence level 1
Operating state Heating
Actual power 6.69 kW
Defrost requirement 6.9%
Last defrost
##########
System settings:
Utility lockout without ZWE
Room station No
Integration Return
Mixing circuit 1 No
Fault without ZWE
Hot water 1 Sensor
Hot water 3 without ZUP
Hot water 4 Setpoint
Hot water 5 with HUP
Hot water + heat pump max 0.0 h
Pump optimization Yes
Access Customer
Monitoring VD On
Control heating circuit Outdoor temp. dependent
Control mixing circuit 1 Outdoor temp. dependent
Boost heating with mixing
Electric anode No
Heating limit Yes
Remote maintenance Yes
Pump optimization time 10 min
Message TDI Yes
Release ZWE 60 min
Hot water reheating No
Hot water reheating max 5.0 h
Smart Grid No
Control mixing circuit 1 fast
VD heating Yes
Temperatures:
Return limit 45.0°C
Hysteresis HR 1.5 K
Hysteresis HW 5.0 K
TR max increase 7.0 K
Release ZWE -2.0°C
TDI set temp 60.0°C
Outdoor temp max 40.0°C
Outdoor temp min -20.0°C
Lowering until -20.0°C
Hysteresis KR 2.0 K
Max. hot water temperature 60.0°C
Min. return set temperature 15.0°C
Pump efficiency:
Heat distribution system Underfloor heating
Control heating Manual
Heating nominal power 100%
Heating minimum power 60%
Control hot water Automatic
dT cooling 5.0 K
Additional heat source 1
Type Heating element
Function Heating and hot water
Position Integrated
Output Out 1
Pump lead flow:
Pump lead flow ZUP 60 s
Priorities:
Hot water 1
Heating 2
Swimming pool 3
System configuration:
Heating Yes
Hot water Yes
FlexConfig:
OUT 2 ZIP
OUT 3 FP1
Heating curves heating 27.5°C
Operating hours information:
Operating hours VD1 5689h
Impulses compressor 1 6327
Average runtime VD1 00:53
Operating hours ZWE1 100h
Operating hours heat pump 5689h
Operating hours heating 4867h
Operating hours hot water 816h
Temperature information:
Flow 28.1°C
Return 25.3°C
Return set 26.6°C
Hot gas 62.3°C
Outdoor temperature -3.1°C
Average temperature -4.7°C
Actual hot water 48.0°C
Set hot water 48.0°C
Heat source inlet -2.6°C
Flow max. 60.0°C
Compressor suction -3.1°C
VD heating 51.3°C
Superheat 7.5 K
Superheat set 7.1 K
TFL1 19.0°C
TFL2 24.5°C
 

T_im_Norden

2021-01-12 10:17:35
  • #6
Do I understand this correctly:
Lstg. Hz. Min. 60%

Does that mean the minimum performance of the heating is 60%?
If yes, reduce it to 20% or so
 

Similar topics
07.10.2016Which heating is recommended for KfW 55?58
02.09.2013Which heating system for prefab houses: air source heat pump, geothermal, solar, photovoltaic17
25.07.2014Energy saving regulation without heating10
21.01.2016Is the heating oversized?44
25.01.2016Which heating system would you choose for our planned new building?15
31.08.2017Do you turn off the heating completely during vacation?24
06.02.2018Solar for hot water/heating or better photovoltaic for electricity?21
01.03.2018Heating reliability during power outage - possibilities?39
13.07.2019It takes a long time for hot water to come27
08.10.2019New heating system with hot water preparation?!20
10.02.2021Air heat pump - increase heating11
09.04.2021Circulation timer on the heater29
08.02.2022How complicated are heat pumps in practical operation?78
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
26.05.2025Which heating system for a multi-family house, heat pump not eligible for subsidies?23
20.09.2023Convert hot water from solar thermal system to photovoltaic system?12
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16

Oben