Heating, something is wrong here. Hallway always 22°..

  • Erstellt am 2022-10-06 08:21:32

Nora22

2022-10-06 17:04:47
  • #1
We had the problem in the kitchen. The chocolate melted in the base cabinets. It turned out that our switches were installed upside down.
 

chewbacca123

2022-10-07 11:41:20
  • #2
By walking into a wall I mean when you come in from outside, from the street. Yes, our hallway is connected by a staircase, ground floor with basement. Next week our sanitation guy is coming by, he wants to take a look at the situation since he has to service equipment here anyway. I can't explain the backflow in the heat at night, yes during the day, but at night? I am curious, I will just measure everywhere now and then we will see. I thank you all for your contributions
 

Alessandro

2022-10-07 12:06:10
  • #3
try something simple first:

check at the heating circuit distributor whether the controller in the hallway really closes the associated valve at the heating circuit distributor (HKV).
You have sight glasses with a flow indicator at the HKV.
If the controller is on MIN or OFF, the flow indicator at the heating circuit hallway should show "0".
 

Alessandro

2022-10-07 12:20:30
  • #4
Turn your HKP down one level. 3L in the bathroom and living area are way too much! You certainly have a very low temperature spread here and the heat cannot be optimally released into the room. Where the "cold" return flow from the living area should actually come back, "warm" return flow is rushing through the hallway!
 

Daniel-Sp

2022-10-07 14:21:15
  • #5
Hi, before simply reducing the flow, the temperature of the return flow at the HK manifold should first be measured. You bought an IR thermometer back then. Just measure at the return flow bar during the heating cycle. And always keep an eye on the total flow when turning down. You have a large heat pump that requires the corresponding flow rate. If you turn down too much, the heat pump will not be able to get rid of the heat and will go into fault mode. When the heating technician was here, check if he reopened the override valve. I'm curious whether the labeling in the HKV was mixed up. Greetings from Hamburg
 

Daniel-Sp

2022-10-07 17:54:29
  • #6


Hi Alessandro
I've thought about this for a while.
But it's not just about the spread, it's also about the volume of water circulated, which results in the amount of heat provided. What's decisive for the heat output from the underfloor heating to the room is rather the temperature difference between the floor covering surface and the room temperature. How the floor covering surface temperature is achieved is ultimately irrelevant. Or am I mistaken?
Could you otherwise provide sources for this statement to read up on? I'm really interested now.
Regards
 

Similar topics
08.01.2018Stairs in the hallway, the floor plan is actually already done :o(20
16.03.2015House entrance with hallway or without15
27.03.2016Air-water heat pump, gas, solar thermal prefab house, advantages and disadvantages?18
17.12.2017Heating circuit distributor - position23
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
05.02.2020LW Heat Pump Alpha Innotec LWDV with 12KW26
16.04.2020Recommendation for digital room thermostat for air-to-water heat pump16
14.12.2020Ice formation brine pipe heat pump78
04.01.2022Air-water heat pump current consumption and data1439
16.10.2020CTA Aeroheat heat pump settings for improvement17
17.12.2020Hallway and living/dining area same flooring?50
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
02.03.2023Heat pump for KfW55 house 148 sqm99
06.04.2023Plan living area floor plan62
24.11.2023Heat pump: buffer tank, capacity and modulation46
11.11.2023Heat pump in the transition period34
13.02.2024Heat pump is not compatible with a water-bearing fireplace144
21.12.2023Power consumption of a heat pump65

Oben