Daniel-Sp
2020-03-06 09:20:19
- #1
Whether the lower modulation range fits, you can find out from the datasheet. The modulation range at different operating points should be indicated there. The lower limit at A7 (7°C AT) would be interesting. Then you can estimate how well the heat pump fits during the transition period. At A-7 you can estimate whether the performance is sufficient in winter or whether the heating element needs to be activated early. Also check the heating load calculation carefully, which room temperature was assumed, does it meet your wishes... Was a room-by-room heating load calculation created with the parameters of your house?