35/28 means that he lets the heating be calculated based on these values.
This means that the installation spacing is chosen so that the house is warmed to standard values with a flow temperature of 35 degrees.
This is no longer up-to-date today; a underfloor heating suitable for a heat pump should be calculated with 30/28.
In addition, you should specify the temperature for the individual rooms, otherwise 20 degrees is assumed for living areas and 24 degrees for the bathroom.
Only when all this, as well as the heating load for each room, is taken into account can one speak of an individual and adapted calculation.