Central room temperature controller for ERR underfloor heating

  • Erstellt am 2020-06-23 11:34:16

Alessandro

2020-07-09 07:12:07
  • #1
It is always a matter of setting
And when everything is perfectly coordinated, then the room thermostat can also make sense. And that even though it is actually only a temperature limiter.
I just wanted to say that you should not imagine the heat pump pushing against the closed valves with swollen hot cheeks while the full volume flow runs through the open valves. It automatically detects the demand through the requirements and regulates itself. This allows a bit of energy to be saved.
 

face26

2020-07-09 09:34:18
  • #2


If your heat pump provides too high supply temperatures, then the heating curve is set incorrectly.

One should read up on hydraulic balancing and the self-regulating effect.

ERR might make sense in rarely used rooms with possibly changing usage types. (Hobby rooms or something like that).

If the balancing has been done properly and the design of the underfloor heating (this is a prerequisite, otherwise it becomes difficult) was done correctly, then the ERR does not have to regulate anything.

Through the balancing I regulate that the individual rooms receive the necessary flow according to their requirements (room-specific heating load calculation). The heating system only provides one supply temperature. Not a different one for each room. In contrast, an ERR opens or closes.
 

untergasse43

2020-07-09 09:49:18
  • #3
Can this ERR/heat pump discussion actually be applied to modern gas heating systems with solar support?
 

Alessandro

2020-07-09 09:50:32
  • #4
The self-regulating effect is amplified by an ERR, which also speaks in favor of thermostats.

Here is an example of what a thermostat can be good for:
Here, the outside temperature has been consistently 15-16°C for a week, sometimes even colder at night. The heat pump is set so that warm water for the underfloor heating is only provided from 18°C outdoor temperature onwards.
However, since it was so warm for weeks before that the masonry heated up and this heat emission still keeps the rooms at 22°C, the thermostats shut the valves.
Therefore, I have no heating demand and the heat pump only heats for the storage.
Of course, the energy for heating the warm water for the underfloor heating would be relatively low due to the heating curve, but the pump would still run continuously and consume electricity. Pumps, efficient as they are, consume relatively a lot of power during operation and are one of the highest wear parts in the system.
 

face26

2020-07-09 09:50:51
  • #5


And if that's the case... you don't need an ERR.

To take another example.

You have 10 rooms. 2 of them currently need 30 degrees supply temperature. But these are the bathrooms, so relatively little volume. All others need less. The heat pump doesn’t differentiate, so you have it set to 30 degrees supply temperature currently. What happens? In 8 rooms the ERR closes. In two it stays open. The heat pump sends out 30 degrees and has a minimum flow rate. It wants/has to get rid of the energy. But it doesn’t because the ERR closed 8 rooms. So what happens?
Depends on the system.
Either you have a heating buffer in between, so the heat pump stores the energy in the buffer. Bad because until it is needed again -> energy loss.
Another or additional way is the bypass valve, so the supply is sent straight back into the return and circulates.

This is a bit exaggerated but is meant to show why ERR usually does not contribute to energy saving.
 

Daniel-Sp

2020-07-09 10:01:14
  • #6
Well, without ERR no heat would be transferred to the underfloor heating and the high return temperature would cause the heat pump to shut down, avoiding the expensive pointless heating of the storage tank. Maybe you can also lower the heating limit, 18°C for a new building is already high, I think.
 

Similar topics
25.11.2015Offer air-water heat pump including underfloor heating, ok?19
12.11.2017Underfloor heating / Wall heating / Ceiling heating - Alternatives?18
30.12.2017Heating system new construction (heat pump + stove + solar)35
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
10.08.2020How to tell if underfloor heating is running - ERR still without thermostat cover50
14.12.2020Underfloor heating heat load calculation - simply explained?26
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
20.01.2021Air-to-water heat pump consumption at 30 kWh per day52
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
25.11.2021Roth heat pump single-family house setting / optimization23
12.11.2021Underfloor heating and heat pump. I thought I understood it15
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
25.05.2022Air-to-water heat pump + underfloor heating + controlled residential ventilation with heat recovery - individually room differently temperature controllable?10
02.02.2023Individual room control with air-water heat pump and underfloor heating20
26.06.2023Heat pump, water storage tank, instantaneous water heater, wfK, underfloor heating, heating and cooling12
07.10.2023How to plan heating with a heat pump in new construction?14
13.02.2024Heat pump is not compatible with a water-bearing fireplace144
22.01.2024Operating costs of air-to-water heat pump, consumption and defrosting16
06.01.20251980s terraced house with underfloor heating - heat pump?10

Oben