Correct.
Plus the fear meter of the builder (or the drilling company )
I also have a brine-water heat pump without modulation and have had similar experiences. About 4-5 cycles per day in winter, without heating operation in summer there are usually 2 cycles (hot water, 180L integrated tank). This results in about 1250 cycles per year. In comparison, the durability is about 100,000 compressor starts. Expected lifespan of the compressor therefore 80 years.
Wear is therefore in my opinion no argument in favor of modulating brine-water heat pumps. That’s why I didn’t choose such a model, it would have cost four digits more. I took a maximally dumb brine-water heat pump
The main advantage is the noise level, as the modulating one often runs quieter. Otherwise, I also think it makes less of a difference.
Although your compressor starts for a non-modulating heat pump are already very very low. Many never come close to that. Many have between 5,000 and 10,000 compressor starts per year. Then durability is indeed a topic.