42,000 kWh of generated heat and only 6,600 kWh of electricity consumption for it can hardly be true.
That would be an average annual performance factor of 6.6.
Common for ground source heat pumps is 4 to 5.5.
The heat demand in typical modern houses is between 6,000-12,000 kWh.
That means your specified generated heat can quite well be correct.
But the required electricity consumption has some kind of error or is there a photovoltaic system on the roof that reduces the electricity consumption especially in summer and on sunny winter days?
That would be an average annual performance factor of 6.6.
Common for ground source heat pumps is 4 to 5.5.
The heat demand in typical modern houses is between 6,000-12,000 kWh.
That means your specified generated heat can quite well be correct.
But the required electricity consumption has some kind of error or is there a photovoltaic system on the roof that reduces the electricity consumption especially in summer and on sunny winter days?
:
I just looked up comparison values:
For a bit under 4 years: 6600 kWh electricity consumption for:
According to heat pump 42 MWh energy (16.2 WW+25.8 heating)
With runtime 4545 hours and under 6000 compressor starts.