My general contractor created an economic efficiency calculation for an LWZ 304 for me at Stiebel Eltron (Stiebel offers a corresponding tool for commercial users, specifically for their own products; to what extent this is beyond any objectivity, you have to evaluate for yourself; the heating load check and comparison of independent offers are still pending in our case).
Kfw55
heated area 140m² (basement, ground floor, attic)
average room height 2.50m
4 people
Building heating load 3.5KW
Standard outside temperature -14°
Heating limit temperature 10° (is this the bivalence point?)
Supply temperature 35°
Coverage rate 98%
LWZ304
Monoenergetic
Bivalence point -5°
Underfloor heating
Domestic water normal demand
Cost LWZ including ventilation system without installation: €19,057 (of which €14,500 for the LWZ itself).
The following economic efficiency calculation (copied from a table, unformatted):
Consumption-related costs Natural gas Heat pump
Energy price heat production [Cent/kWh] 7.50 19.00
Energy price auxiliary energy [Cent/kWh] 25.00 25.00
Base price per year [€] 205.00 67.00
Energy costs of the system [€] 833.00 539.00
Energy costs/living area [€/m²] 5.95 3.85
Operating costs Natural gas Heat pump
Maintenance and repairs [€/year] 25.00 10.00
Cleaning of the flue gas system [€/year] 75.00 0.00
Operating costs of the system [€] 100.00 10.00
Total costs Natural gas Heat pump
Consumption- and operating costs [€/year] 933.00 549.00
Investment costs [€] 19,700.00 25,657.00
Capital-related costs [€/a] 1,450.00 1,888.00
Maintenance costs [€/a] 385.00 95.00
Total costs of the system [€/a] 2,768.00 2,532.00
Total system costs/living area [€/m²*a] 19.77 18.09
Amortization Your data
Observation period [years] 20
Amortization [years] 14
Boundary conditions Your data
Observation period 20
Interest rate 4
Price increase natural gas %/year 5
Price increase heat pump electricity %/year 2
Criticism points:
- I assume that installation costs are not included here?
- no exact information about the GAS system
- Price increase for natural gas was estimated at 5% and electricity at 2%
- Can the bivalence point be set freely? Does -5° make sense here or is this also a manipulated calculation?
- What is the durability of the devices? If I have to replace my heating every 20 years, I don’t gain much if the break-even is only after 15 years
- Domestic water consumption is stated as normal, what does that mean? No bathing allowed and only 5 minutes shower per person?
As mentioned, an independent heating load calculation still has to be carried out and then I will get separate offers from building services companies.