Your statement is interesting. I have a heating load calculation for our KfW Efficiency House 55 EE, which is being built as a bungalow (90 m²). Unfortunately, the desired flow temperature of 30° was not achieved. It ended up being 33°. The temperature difference is 6 degrees; by increasing the volume flow, I can already achieve a better flow temperature at 32/28.
In the heating load calculation, floor coverings of parquet and thick tile were set as a standard. Now we will use design vinyl throughout. According to your statement, I should be able to achieve the flow temperature of 30° with this?
Vinyl and tile are quite similar in terms of thermal conductivity, but only if the vinyl is glued without a carrier.
Floating on a carrier, it is more comparable to laminate.
And the flow temperature is not as static as it sounds now, because it is always to be seen in relation to the outside temperature.
However, it is quite possible that 2 degrees less would be sufficient for you now when switching from parquet to glue-down vinyl!
But, of course, this only applies if that was really the room determining the flow temperature.
If, as usual, the bathrooms have the deficiency and are tiled there, you actually gain nothing from the change.
Because a surface heating system is always only as good as its weakest link. ;)