can someone among the experts here evaluate the Vaillant arotherm 75/6? it’s supposed to easily achieve the annual performance factor, even 4.6. but here in the forum you rarely hear about Vaillant in connection with heat pumps... is there a particular reason for that?
I myself have a Vaillant Arotherm split with Unittower... but it’s only been in the house since April, so I can’t say anything about consumption in winter yet.
I have a calculated heating load of 3.5 kW and the general contractor/house manufacturer wanted to install a 5 kW system. However, I insisted on installing the smallest possible system (I believe 3.5 kW) and got it. All in all, it seems to be a solid product, but we’ll have to wait for winter.
In addition to optimal performance relative to the heating load, there is the modulation range of the system and the design of the underfloor heating.
I also insisted on a max supply temperature of 30°C at NAT and max 10 cm pipe spacing and got that despite pressure and manipulation over the temperatures. Otherwise, I would have gotten a 35°C/28°C standard layout with 15 to 20 cm pipe spacing.
In general, you have to engage intensively with the systems yourself and read up, because the standard builder, house manufacturer and their subcontractors usually no longer explain during commissioning how to set the room temperature and hot water temperature. Let alone how to deactivate the electric heating element, lower the heating curve, or put the system into whisper mode which makes it modulate even a bit more.
Unfortunately, I couldn’t argue away the individual room control and mini return buffer tank. But I disconnect the actuators and luckily the buffer is only 15-20 liters.