Air-to-water heat pump sizing in new construction

  • Erstellt am 2020-08-06 11:45:28

Pixelsurium

2020-08-06 22:39:29
  • #1
here as JPGs



 

Pixelsurium

2020-08-06 22:40:31
  • #2
The only thing I can find about the outside temperature there is this:

What do you want to know about the house? It has no basement and is apparently "better" than KFW 55. Location Baden-Württemberg near Heilbronn. Timber frame construction with wooden facade.
 

Daniel-Sp

2020-08-06 23:12:41
  • #3
I have never understood these energy saving ordinance calculations. They are of no use to you either. You need the heat load calculation according to DIN 12831 or something like that. Then you select the heat pump capacity based on that, not according to some energy saving ordinance calculations. If you know the following data, you can estimate it quite accurately. Transmission heat transfer coefficient=Ht-value Building envelope area NAT Desired temperature in the house Heated gross volume Number of occupants Type of ventilation
 

Pixelsurium

2020-08-06 23:30:47
  • #4


Building envelope area: 559.65 m2
Building volume: 726.44 m3
Heated air volume: 552.09 m3
Useful building area: 232.46 m2
A/V0 ratio: 0.77 1/m
Window area: 30.41 m2

Desired temperature: 20-21°C
Occupants: Currently: 2 + 1 child + possible granny flat (let's assume max. 5-6)
Ventilation: None

I don't know where to get the Ht value and NAT from?

I will try to request the heating load calculation. I find a 10 kW air-water heat pump for a new building quite extreme... that's why I got suspicious.

Regards
 

Daniel-Sp

2020-08-06 23:33:47
  • #5
NAT is the standard outside temperature HT stood for me in the KfW certificate
 

Pixelsurium

2020-08-06 23:36:53
  • #6
NAT: -14W Unfortunately, I do not have the KfW certificate because we waived the subsidy.
 

Similar topics
29.04.2010Energy Saving Ordinance 2009 even without solar?16
07.03.2012New construction: Energy saving certificate / Energy performance certificate, verify costs15
28.02.2013Heat demand calculation according to DIN 1283112
07.06.2013Is it mandatory to build according to the Energy Saving Ordinance (2009)?12
24.03.2014Heating proof: Heat load calculation according to DIN 12831 or DIN 4708?10
23.10.2016Thermal insulation, Energy Saving Ordinance, KFW 70 / 55 / 40 - Your experiences31
19.06.2015Build according to KFW 70 or the Energy Saving Ordinance 201442
15.12.2019Aerated concrete exterior wall vs. Energy Saving Ordinance13
09.07.2015Energy Saving Ordinance Proof vs. Energy Saving Ordinance Proof + KfW-70 Proof13
19.10.2015New energy saving regulation from 2016 -> What to build?30
23.10.2015Energy Saving Ordinance 2014 - Gas boiler without solar?38
16.07.2017Energy Saving Ordinance, KFW55, KFW40 or KFW40 Plus19
21.04.2019Floor plan planning shortly before submitting the building application1420
10.10.2018General Contractor Offer - Heating + Sanitary = OK?16
05.01.2020Gas heating + photovoltaics possible without proof15
04.02.2020Whom to entrust with the room-wise heating load calculation?46
04.05.2020Energy Saving Ordinance or Thermal Insulation Certificate Offer17
05.06.2020Heating load calculation or room heating load26
14.12.2020Underfloor heating heat load calculation - simply explained?26

Oben