Air-to-water heat pump sizing in new construction

  • Erstellt am 2020-08-06 11:45:28

nordanney

2021-07-07 23:05:58
  • #1
It might be attempted with some, but most (good) heating installers won’t sell you a buffer.
 

Deliverer

2021-07-07 23:10:50
  • #2

Since apparently not only narrower (and longer) but also more circuits have been installed, this should not be a problem. And you can throttle them down to zero if necessary.
If you can lower the supply temperature far enough, this is not even necessary. Then it regulates itself: the room is warm, heat transfer from the floor to the room no longer occurs because the delta T is too small. Flow rate does not matter. But this only works with small installation distances. So congrats. ;-)
 

tomtom79

2021-07-07 23:19:02
  • #3
We already had a person including walls before, who was that? As a reference, we have about 250 sqm of heated area but Kfw 70 and an 8 kW heating system. A 6 kW one would have been more than enough.
 

RotorMotor

2021-07-07 23:23:14
  • #4
I would also say that it is even a bit better with VA10 and 6 circles than VA15 with 4.

Since the bathroom is usually the "problem room," it would most likely not have been necessary, but you don't look a gift horse in the mouth, ...
 

OWLer

2021-07-08 12:38:13
  • #5


So, I was able to solve the mystery. The installers on site are working according to old plans. As described above in the quote, the calculation was optimized last year because we were within the maximum volume flow range of the 75/6 with a spread of 4K and a flow temperature of 33°C. As a bonus, the balancing of the heating circuits in the WEK was also eliminated, as the number of heating circuits there could be reduced from 6 to 4.

The message therefore did not make it into the execution, although I had sent the plans again to both the site manager and the plumbers during the discussion about the wall heating.

Well, since that was the only change from the initial planning, my focus now is to pay attention to minimizing the heating loop distances upstairs in the bathroom. The rest should be fine; I will just have to throttle more in the WEK or else I will get grilled during the hydraulic balancing. I’d just have to send my wife on vacation for that time or something, because she will surely tear my head off during the hydraulic balancing since it won’t amuse her much to be constantly freezing and sweating alternately. :)
 

OWLer

2021-07-08 21:41:45
  • #6
In the upstairs bathroom, the small area has been quite well utilized in my opinion. Unfortunately, the general contractor did not want to completely relocate the shower, even after long discussions, nor under the bathtub. Upstairs, the 5cm was still quite well achieved.



For the downstairs toilet, I roughly estimated about 7cm (should be 5cm). Except for the hallways and bathrooms, everything is now completely done with 10cm and looks really good in my eyes.

 