It might be attempted with some, but most (good) heating installers won’t sell you a buffer.That is also my understanding so far. However, it would mean that everyone would then also get the buffer tank an
It might be attempted with some, but most (good) heating installers won’t sell you a buffer.That is also my understanding so far. However, it would mean that everyone would then also get the buffer tank an
My concern is how far the modified heating circuits can be throttled and how that affects the head pressure or the flow rate under stress.
We already had a person including walls before, who was that? As a reference, we have about 250 sqm of heated area but Kfw 70 and an 8 kW heating system. A 6 kW one would have been more than enough.5cm :) in the bathroom, 4 circles on 15 sqm. I want to see something like that :)
So, I have received feedback from the engineering office regarding the smaller Vaillant. They increased the flow temperature from 33 to 33.5°C and the return temperature from 29 to 28.5°C, thus increasing the spread from 4 to 5 K.
Now the volume flows are lower and the small 75/6 A from Vaillant can deliver the volume flow.
Let's see how I can optimize this in the long term. It almost feels like an old building with 34°C flow temperature when I compare the benchmarks here with you. Our building structure with gables and bay windows plus many floor-to-ceiling windows really seems to make a big difference. But I hope for good solar gains in practice so that I can lower the flow temperature over the years.
The only downside is that I can't get the small 55/6, which would be perfect for our heating load, above an annual performance factor of 4.5...