Hello everyone,
we are also currently in the process of deciding on an air-to-water heat pump, but I am a bit overwhelmed because the offers vary greatly.
Our single-family house (KfW55) + granny flat and basement apartment will have a total of about 290m² of heated space. According to the Energy Saving Ordinance, the heating demand is 0.276 W/(m²K). According to my calculation, that would be 8kW. If I assume 6 people x 0.25kW for hot water, that adds another 1.5kW, so a heat pump with 9.5 - 10kW should be sufficient.
Where is my thinking wrong? One provider offered me a 14kW Daikin 3M heat pump. Did he simply ignore my Energy Saving Ordinance and assume a too high heat demand, or am I missing something?
My second question concerns the buffer tank: One provider says that a 100l buffer tank is sufficient because the underfloor heating already stores a lot of water, another says that 500l are needed to keep the cycling low. I would really appreciate your assessment.
Best regards