Air-to-water heat pump sizing in new construction

  • Erstellt am 2020-08-06 11:45:28

T_im_Norden

2020-11-09 20:31:35
  • #1
Anhydrite screed is generally considered well suited for underfloor heating due to its good thermal conductivity
 

OWLer

2020-11-13 12:29:22
  • #2
So, I now have the offer from the heating engineer. Looks quite reasonable. However, I am now in a dilemma.

He wants to install the Vaillant Arotherm VWL 105/6 A, which with 10kW heating capacity is significantly larger than our heating demand of 5.9 for heating + 0.8 (estimated) for hot water = 6.7kW according to NAT.

"Actually," the smaller VWL 75/6 A should easily be sufficient and even have reserves. Based on what I have read here, it would still be too big.

However, I am now unsure about the pump flow rates.

VWL 105/6 A: 1418 l/h (788 mbar)
VWL 75/6 A: 790 l/h (640 mbar)

Heat load calculation resulted in:

Pressure loss in the most unfavorable circuit: 7879 Pa
Pump head: 0.79 m
Total flow rate: 22.2 l/min
Total flow rate: 1331.3 l/h

As a layman, I conclude that while the heating capacity of the smaller heat pump would easily suffice, the circulation pump would then be too weak to pump the warm water through my many and long heating circuits – I would have to bite the bullet and take the larger one with the risk of short-cycling, etc.

Did I understand that correctly or am I making a conceptual mistake?

Can I see anywhere how far the large Vaillant can modulate down?
 

T_im_Norden

2020-11-13 12:51:36
  • #3
Vaillant states a maximum volume flow of 1205 liters for the 75. You are then a bit above that.

The 55 goes down to 2.10. The 75 goes down to 3 The 105 goes down to 5.40

As a layman, I would even tend towards the 55, but the volume flow no longer fits there.
 

OWLer

2020-11-13 12:57:28
  • #4
Thank you for the feedback, may I ask where you found the information? I usually don’t have much trouble googling, but when it comes to all the [Haustechnik] topics, it seems there are different circles....
 

Tolentino

2020-11-13 13:06:50
  • #5
According to the annual performance factor calculator, the 55 model does not achieve 4.5 at least.
 

OWLer

2020-11-13 13:17:27
  • #6

Thanks for the hint. With my supply temperature and hot water proportion, I already reach an annual performance factor of 4.7 with the 75.
 

Similar topics
06.12.2015Heat pump / final energy demand / annual performance factor20
21.06.2016Heat pump with photovoltaics vs gas and solar thermal52
24.01.2020Annual performance factor calculation for funding (parameters and calculation tool)29
01.12.2020Eligible costs for heat pump134
08.05.2021New construction - floor heating unevenly hot (Vaillant aurocompact)12
09.11.2021Cost maintenance Vaillant Therm plus VWL 75/6 A Height ok?20
30.11.2022Controlled Residential Ventilation & Heat Pump: Viessmann vs. Vaillant vs. Zehnder?47
11.08.2023Purchase advice, heat pump comparison: Daikin or Vaillant?19

Oben