I think gas is not a disaster. Unlike existing buildings, with an [Energieeinsparverordnung] house you have a relatively low heat demand. Therefore, gas consumption is also limited.
I find it important to build the underfloor heating in such a way that switching to a heat pump is possible without problems. Low supply temperature of max. 30 degrees, preferably equally long heating circuits, room-by-room heat load calculation, … I would take care of that sooner rather than later, and overall you will have to study the topic more if you don’t want something 0815.
I find it important to build the underfloor heating in such a way that switching to a heat pump is possible without problems. Low supply temperature of max. 30 degrees, preferably equally long heating circuits, room-by-room heat load calculation, … I would take care of that sooner rather than later, and overall you will have to study the topic more if you don’t want something 0815.