I still consider the 18kw to be too high. If you can provide some information about the aerated concrete block, the window areas/geometry, I can roughly calculate whether this could be correct.
Thanks for the offer.
I can now provide the following more detailed information:
- All exterior walls are built with Ytong at 36.5cm, also in the basement (black tank)
- The geometry is mostly cubic, except for the ground floor, where the house has an L-shape (approx. 28 sqm attached to a cube of approx. 130 sqm)
- The house is now fully basemented, so also L-shaped
- On the upper floor, at the L position, there is a roof terrace with about 28 sqm accordingly
- Attic purely cubic with a hipped roof
I have now learned the corresponding U-values and recalculated the envelope areas myself (which almost coincide with the details in the heating load calculation, so that is at least okay):
- 154.40 sqm with Uw 0.21: basement floor slab
- 150.80 sqm with Uw 0.18: exterior wall in the basement (net, i.e. without windows and doors)
- 227.40 sqm with Uw 0.21: exterior wall ground floor - upper floor (net)
- 174.66 sqm with Uw 0.17: attic / roof (net)
- 118.30 sqm with Uw 0.86: window areas (mostly safety glass)
- 10.30 sqm with Uw 0.7: exterior doors (Uw estimated here, as I have no data)
- 28.02 sqm with Uw 0.24: roof terrace areas upper floor
In total, about
860 sqm envelope area and naively calculated an average
U-value of about
0.29 (which is given as 0.34 in the heating load calculation) — thus differing by about 15% (in contrast to the envelope area). Unfortunately, the heating load calculation does not specify individual U-values, only the average U-value, so I currently do not know how the difference arises.
Do you think the above U-values correspond to the standard, or does one of the values deviate from the usual range? Unfortunately, I have no experience with this so far...
However, I do not know how to get from the envelope area and the U-value to the heating load. As far as I know, one also needs the
building air exchange, which is assumed to be
0.6/h in the heating load calculation, as well as the
minimum outdoor temperature, which is assumed to be
-14°C. The
room interior temperature is
20°C and the
heated net volume 1230m3,
gross volume 1620m3.
Many numbers to keep track of ...