Thank you for the suggestions.
I am currently trying to read up on and understand a few things.
So that I can then make a decision.
1. Heating load
I assume that the heating load calculation from the MEP office, which we have on hand, is correct.
(With the data known to the MEP planner up to that point)
Standard heating load: 5115 W
Norm heating load: 6233 W (includes a pre-heating surcharge of 1118 W on the standard heating load)
2. Improvement of the building fabric
Our heating load is probably somewhat lower, since we, for example, upgraded the front door from double glazing to triple glazing. In the MEP planning, a U-value of 1.5 was assumed for the door, this was before the upgrade. Now the two fixed glazed side panels have a Ug value of 0.6 (glass) and the front door panel 0.8 (Ug).
Then we want to additionally insulate the topmost floor ceiling. Towards the unheated attic (used for storage), we have laid or plan to lay 10 cm of mineral wool WLG 0.35 on top of the existing floor ceiling (plasterboard, vapor barrier, 20 cm mineral wool WLG 0.35, spruce beams). The material is ordered. According to Ubakus, the U-value will go down from 0.194 to 0.132. The heating load calculation assumes a U-value of 0.210. That probably includes thermal bridges. The attic stairs are also still included. Nevertheless, in the future, it will be less than 0.210.
[IMG alt="Bildschirmfoto 2022-12-11 um 11.49.44.png"]https://www.hausbau-forum.de/data/attachments/76/76182-e9d40a7d676d49270c27df85da07d2ae.jpg[/IMG]
3. Design of the underfloor heating
We can no longer change anything about the pipes. The pipes are laid, the screed is in.
We do not know how long the individual heating circuits are. The laying distances are very clear. 15 cm, somewhat less in the bathrooms.
Heating circuits:
Ground floor
1 guest WC
1 utility room
1 hallway
1 guest room
3 for open plan kitchen, dining, living
Upper floor
1 bathroom
1 corridor
1 bedroom
1 study
1 child’s room
1 hobby room
WC and bathroom each have an electric auxiliary heater
4. Refrigerant lines
The outdoor and indoor units of the heat pump are not planned wall to wall. (due to acoustic and floor plan reasons)
From the utility room, refrigerant lines run in the screed through the bathroom to the exterior wall. That is maybe a total of 6 m refrigerant lines, considering the height differences in the wall and at the indoor unit.
For this reason, a monoblock system is probably no longer possible, right?
5. Ventilation
We do not have one, windows open and cross ventilation.
6. Planned heat pump
The planned heat pump seems to be designed for monovalent operation, and somehow the MEP planner arrives at 11 kW with the "Heating Solutions Navigator."
[IMG alt="Heizen.png"]https://www.hausbau-forum.de/data/attachments/76/76183-6d34e9489a63f5085cfa6ae15de41c38.jpg[/IMG]
[IMG alt="Heizen-Loesung.png"]https://www.hausbau-forum.de/data/attachments/76/76184-7f5a4fe835de9e9061d67ca1c7f86c24.jpg[/IMG]
From the 5.1 kW, he arrives here at 7.48 (however that may be) as required heating capacity. (Well, hot water still has to be added to the heating load)
Then at 8.31 kW as the heating capacity of the heat pump at -8.6°C as min ambient (whatever that means)
and then goes to the next available heat pump size with 11 kW at Daikin.
Here again the comparison via an online tool which was recommended:
[IMG alt="Bildschirmfoto 2022-12-11 um 12.48.42.png"]https://www.hausbau-forum.de/data/attachments/76/76186-0b6121745680be44dba7b2f2be0471bd.jpg[/IMG]
I only found the transmission heat transfer coefficient in the building energy law planning.
Building envelope area and heated gross volume taken from the MEP planning.
22°C is a very cozy temperature for us.
6. Decision?
I am not a professional, but I would think that a 6 kW system would serve us well.
We can no longer optimize anything on the heating circuits, so a 4 kW system might be too tight.
The Daikin has a 180 l hot water tank.
We are 3 people, if we calculate 1 kW hot water load instead of 400 W, since the tank is a bit small, we end up at just under 5 kW.
Am I thinking correctly here, or am I missing something?
Thanks to you all.