Tasks of the EEE in BEG individual measure (Bafa)

  • Erstellt am 2025-04-10 17:56:31

kettjen

2025-04-10 19:22:16
  • #1
We had an extensive roof renovation carried out for a house with an extension (new construction of the roof truss on one part of the building, conversion from a pitched roof to a flat roof on the other part of the building). To receive the subsidy, we hired an energy consultant. Scope of services: checking the offers for eligibility for funding, application submission, checking the invoices. According to him, the offers are eligible for funding.

In addition, he is preparing the thermal insulation certificate for the building authority.

The measure is almost completed and he is now preparing the thermal insulation certificate. In doing so, he mentioned that he has now noticed that there will be massive condensation in one roof structure and that the other roof structure accounts for a comparatively large proportion of the building envelope, so a ventilation concept for the attic might possibly need to be made.

Shouldn't these two points have been noticed during the offer review?

It is clear that he should not provide me with a finished ventilation concept, but at least a hint like "hey, you probably need active ventilation here, better plan for it or let us calculate it" BEFORE everything was built would have been good. Now I have to reopen parts of the roof to replace the insulation (PIR to mineral wool because of the dew point) and to provide ventilation slots.

He said that this is not part of the BEG EM funding, but that he would look at the condensation as part of an energy consultation and the ventilation issue in an iSFP.
 

kettjen

2025-04-10 19:51:50
  • #2


Where does it say that the concept is mandatory for new windows or analogously for all other measures?

Our roof renovation includes a new roof structure including insulation, new floor ceiling, partial changes to the exterior walls, dormer, terrace door, etc. So actually almost every building component group is involved.
 

SoL

2025-04-10 20:44:01
  • #3

DIN 1946-6

According to the commissioned scope of services, your energy consultant does not have to do anything there. He only checks whether the offers are eligible for funding. If, when checking the U-value, he notices that the construction is nonsense and tells you, that is benevolent kindness.

The planning and checking of the construction can be commissioned, for example, it was part of the preparation of the iSFP in our case.
Who planned for you? That person is responsible, provided they were commissioned for it. With such a conversion, you certainly do not let the contracted construction companies / craftsmen do that, do you?

Because they usually have something like this in the fine print:
 

nordanney

2025-04-10 20:58:48
  • #4

This is an indirect requirement from the Building Energy Act (§13) and the DIN mentioned by .

I'll just boldly ask now, who took over the planning services? The energy consultant only checks whether the measures are eligible for funding (U-values etc.). You can build complete crap that is eligible for funding but technically a disaster.
 

kettjen

2025-04-10 21:11:59
  • #5
We had an architect with us who then involved the energy consultant for all the topics.

So what about the part in the guideline: The energy efficiency expert must provide at least the following services as part of the support of the construction measure during the energetic renovation with individual measures and confirm their program-compliant implementation

And further: explain the eligible costs as well as confirm compliance with the technical minimum requirements according to the BEG EM for this measure

First sentence of the technical minimum requirements (which are to be confirmed as part of the TPB): In renovation measures – especially on the heat-transferring building envelope – it must always be checked whether measures for moisture protection, in particular to prevent condensation and mold growth by maintaining the minimum air exchange and minimum thermal protection in connection with the renovation measure, are necessary.
 

SoL

2025-04-10 21:43:36
  • #6
Why are you fixated on the energy consultant? If the construction is botched, your architect has failed. Approach him. You have better chances there...
 

Similar topics
17.12.2015Kfw funding 2016 - How to set up construction financing?10
29.06.2016Promotion of soundproof windows11
24.05.2018Connecting two houses - How to design the renovation?12
13.06.2018Energy consultant for a KfW 70 house costs 2,500€?29
15.02.2020KFW55 funding + BAFA funding57
20.01.2020New BAFA funding - Air-to-water heat pump with solar thermal39
09.02.2020BAFA - Funding: House contract before application submission?10
16.06.2021Smart Home Promotion New 02/2020103
08.05.2020New construction - Is an energy consultant worthwhile?12
03.06.2020KfW 55 + BAFA Funding - Costs and Subsidies24
13.09.2020BAFA funding for heat pump (air-to-water heat pump) when building with a developer25
19.05.2021Promotion of e-mobility for new construction118
14.02.2024Bafa funding for heat pumps will be discontinued as of 31.12.2020.510
20.04.2021BAFA funding depends on the form "Confirmation of the Developer"20
08.05.2021New building with granny flat - general contractor restricts rental and KfW funding51
27.02.2023Conversion of two-family house to single-family house - floor plan?29
06.02.2022New Construction KfW 55 EE: Different opinions between energy consultant and general contractor27
07.05.2022KfW stop! Energy consultant wants his money!61
30.06.2023Conversion of a two-family house into a duplex with complete renovation12
11.12.2024Current energy consultant costs31