*Dipol*
2021-01-17 01:05:04
- #1
The sketch clears the fog.
A cable routing through the lightning protection zone LPZ 0A and even on the outside of the facade through the grounding-required 2 m area shows a lack of lightning protection awareness by the installer and could only be topped by cable installation next to a metallic roof gutter (Please provide a photo of this).
Even if this antenna location, which is unfavorable in terms of HF and lightning protection, was specified by the client for aesthetic reasons, a standards-knowledgeable antenna installer should have raised concerns against an installation without lightning current capable grounding and equipotential bonding and should have refused the installation in this form. Direct lightning strikes are fortunately rare, but if St. Florian (the patron saint of firefighters) fails, no one will remain dry here. A basic protection against electric shock is also missing.
In order to propose a standards-compliant solution in detail, information is still required on whether the equipotential bonding, which has been mandatory since the expiry of the transition period in 1990, has been performed and please also add the position of the HES (with grounding system?) in the sketch. Pictures of the decommissioned cable TV system and the "bare" HES without cover would avoid further inquiries. The type and approximate length of the coaxial cables are also relevant.
[*]The satellite antenna at this position is clearly subject to grounding according to IEC 60728-11 and
[*]the cable routing upwards along the facade also crosses the 2 m zone below the eaves, which is normatively defined as not strike-protected.
[*]A cable TV signal feed from HÜP -> HAV -> new directional coupler pass-through junction box -> one of the existing satellite cables -> cable TV quad splitter in the attic -> new pass-through junction boxes + terminating resistors is technically possible.
[*]Subject to the approval of the cable network operator, satellite signals may also be injected into the other cables, except for the satellite cable repurposed for the cable TV feed, as long as the cable TV area does not use the range up to 1006 MHz.
A cable routing through the lightning protection zone LPZ 0A and even on the outside of the facade through the grounding-required 2 m area shows a lack of lightning protection awareness by the installer and could only be topped by cable installation next to a metallic roof gutter (Please provide a photo of this).
Even if this antenna location, which is unfavorable in terms of HF and lightning protection, was specified by the client for aesthetic reasons, a standards-knowledgeable antenna installer should have raised concerns against an installation without lightning current capable grounding and equipotential bonding and should have refused the installation in this form. Direct lightning strikes are fortunately rare, but if St. Florian (the patron saint of firefighters) fails, no one will remain dry here. A basic protection against electric shock is also missing.
In order to propose a standards-compliant solution in detail, information is still required on whether the equipotential bonding, which has been mandatory since the expiry of the transition period in 1990, has been performed and please also add the position of the HES (with grounding system?) in the sketch. Pictures of the decommissioned cable TV system and the "bare" HES without cover would avoid further inquiries. The type and approximate length of the coaxial cables are also relevant.