If the grounding in the base slab is BELOW the sealing in natural soil (also below the bitumen sealing and the blinding layer), that is correct for now.
This is then a ring ground electrode which, since the obsolete DIN 18014:2007-09, must consist of corrosion-resistant stainless steel, material number 1.4571 (V4A), min. 10 mm round or 30 mm x 3.5 mm flat. In the reinforcement of non-earth-contacting foundations/base slabs, a functional equipotential bonding conductor must also be installed LIKE a foundation earth electrode and connected every 2 m to the reinforcement as well as each connection tab or max. 20 m building perimeter to the ring ground electrode. The maximum mesh size for both systems is 20 x 20 meters.
The grounding resistance can be proven by measurement, should be done, and is part of it.
Measuring the soil resistivity is useful, but since the first
VDEW guidelines for embedding foundation earth electrodes in building foundations from 1964 over obsolete DIN 18014 predecessors, curiously
NO obligation. Even with lightning protection systems, the previously obligatory > 10 ohms is now only a recommended guideline. With and without lightning protection systems, measuring continuity resistance is mandatory. The value has changed from ≤ 1 ohm to currently ≤ 0.2 ohm. Lightning protection systems are only required by building regulations for certain buildings but may be advisable after elaborate risk analysis according to IEC 62305-2. This is practically only possible software-supported with the DEHN toolbox, which only a few roofer companies active in lightning protection possess and master. For photovoltaic systems, a lightning protection system may be required from ≥ 10 kW from an insurance law perspective and not only from 30 kW if the non-binding VdS guidelines are contractual. With a lightning protection system, a closer mesh size of max. 10 m x 10 m is required for ring ground electrodes, and the connectors must be certified according to IEC 62561-1 as lightning current capable. Photovoltaic modules are protection insulated, which is why, contrary to frequent claims, without a lightning protection system no equipotential bonding of the frames is normatively required.