My electrician explained to me that we have to ground the gutter and the exterior stainless steel chimney via the foundation earth electrode erden müssen.
Whether this electrician belongs to the approximately 20% of the guild who still faithfully hold a VDE subscription selection for electrical engineering crafts, you have to determine yourself. However, even electricians with such a subscription are not lightning protection specialists, and where building regulations do not require a lightning protection system, there is no obligation to ground gutters or downpipes.
Nevertheless, it is sensible to design grounding systems so that they can also be used later for a lightning protection system and to plan connection lugs for a lightning protection system with minimal additional cost during the installation of the grounding system. In that case, the downpipes should also be connected with the connection lugs.
The solar system on the roof can then also be grounded via the gutter. The argument: In the event of a lightning strike on the solar system/chimney, it is safer if the current is conducted outside the house.
Lightning currents use every path to earth. They distribute almost independently of cross section according to the inductive resistances in loop conductors and will not fulfill the wishful thinking of only discharging on the outside even with exceptionally lightning current-capable connectors.
The company that created the base plate was willing to lay all the connections in the foundation to the outside, but said I should think it over carefully.
Google "DIN 18014:2023-06" and check whether this company even meets the requirements for the installation and documentation of earth electrodes.
It was stated here that grounding is not necessary. On the contrary: if it is grounded, the system must be checked regularly. If this does not happen, there can be trouble with the insurance in case of damage.
Lightning protection systems have no eternal life and must be maintained at intervals. With a lightning protection system, a functional grounding of the module carriers according to DIN VDE 000-712 and DIN EN 62305-3 (VDE 0185-305-3, supplement 5) is mandatory; without a lightning protection system, contrary to frequent incorrect statements, it is not.
IF a functional grounding is installed, then according to German standards it must be routed directly adjacent to the photovoltaic lines, which excludes the option with the downpipe.
See the DEHN lightning planner for this. Even with at least 2 down conductors for a lightning protection system, functional grounding conductors of at least 6 mm² (separation distance maintained) or 16 mm² Cu (separation distance not maintained) are normatively required.