Is a buffer tank useful in a heat pump?

  • Erstellt am 2024-02-14 15:05:39

hanse987

2024-02-14 17:47:17
  • #1

Why do you want a 12 kW "monster"? Don't oversize the heat pump! Even the calculated 8 kW feels too large to me. Is there a room-by-room heating load calculation?
 

jx7

2024-02-14 19:07:02
  • #2


I already have a modulating heat pump with 3-12 kW.

The consideration is to retrofit a buffer tank.
 

RotorMotor

2024-02-14 20:17:39
  • #3
How do you come to think you might need one? Does the heat pump cycle too frequently for you? Is the consumption too high?
The heat pump is probably significantly oversized.
First of all, you should check if it is really a problem and if so, whether it can be controlled with settings.
 

k-man2021

2024-02-14 21:10:00
  • #4

That means the house and heating system are already built or installed and you want to change something, or have you only ordered/bought the heat pump so far? Maybe you would like to describe the initial situation in more detail so that you get meaningful answers…
 

k-man2021

2024-02-14 21:17:55
  • #5
Just to clarify: our architect and the heating planner were completely in agreement and roughly recommended the following to us: heat pump, stratified storage tank and fresh water station, no buffer, no ERR.
 

jx7

2024-02-14 22:58:17
  • #6


1) House & heat pump are 7 years old. The heat pump made 24 starts per day, now the compressor is broken, I have already discussed everything. One solution option is a buffer tank. Since I don't want the discussion to get out of hand and I specifically want to learn something about the topic of buffer tanks, I have formulated the inquiry this way.

2) "Stratified storage tank and fresh water station, no buffer"

Huh? A stratified storage tank with a fresh water station is a buffer tank after all.
 

Similar topics
01.08.2014Water-bearing wood stove (supplement to the air-water heat pump and controlled residential ventilation with heat recovery)?10
12.09.2014Domestic Hot Water Heating vs Efficiency of Air-to-Water Heat Pump11
23.02.2015Air-water heat pump with solar thermal and fireplace? Cost/benefit/meaning34
19.05.2021Experiences with brine heat pump491
24.06.2016Which storage should be used with an air-to-water heat pump?16
29.04.2018Gas heating + solar & controlled residential ventilation or air-water heat pump Energy Saving Ordinance 201626
23.01.2020Towel radiator for air-water heat pump22
22.11.2019Feedback on heat pump / offer requested!46
24.02.2020Freshwater station and buffer tank: technically better choice?24
11.06.2020Active cooling function heat pump or air conditioner in new construction12
14.10.2022Air-to-water heat pump sizing in new construction311
19.02.2021Combine heat pump and water-bearing fireplace60
26.04.2022Air-to-water heat pump without buffer storage | Heating installer refers to building energy law requirement33
12.04.2022From when is a heat pump worthwhile in an old building?13
31.03.2022Air-Water Heat Pump - Buffer Storage Yes or No?28
08.06.2022Distance of buffer tank to ground source heat pump19
02.03.2023Heat pump for KfW55 house 148 sqm99
24.11.2023Heat pump: buffer tank, capacity and modulation46
13.02.2024Heat pump is not compatible with a water-bearing fireplace144
02.02.2024How much buffer storage is needed for approximately 300 m²? Is cooling worthwhile?11

Oben