The heating system is now defective. Presumably, the compressor has given up due to far too many starts.
Unfortunately, the installing company Brunnenbau Heth from Lorsch refuses to carry out the repair, citing a shortage of skilled workers. Two other Ecoforest partners in the area have also declined because they are unable to replace the compressor. Ultimately, someone from the German branch of Ecoforest in Wangen (400 km away) will come on Monday to replace the compressor for around €5,000.
In the meantime, I have received a list of possible causes of error from a heat pump specialist. I have written to the company coming on Monday asking them to please check the following points:
- Check and, if necessary, clean the dirt trap in the heating circuit
- Check and, if necessary, clean the dirt trap in the brine circuit (hot gas monitoring)
- Check temperature sensors (flow temperature and return temperature)
- Check bypass valve (possibly too far open?)
- Optimize speed control so that lower speeds are reached, possibly speed limitation (heating demand of the house is 7-8 kW, heat pump modulates nominally up to 12 kW, in practice even higher?)
- Optimize hydraulic balancing (noticeably less heat reaches the upper floor than the ground floor when all individual room controllers are open)
If an error is found this way, we would save the buffer tank. A correctly adjusted, modulating brine heat pump with underfloor heating should actually also work without a buffer tank; with two neighbors with the same construction company and identical Ecoforest heating, it works perfectly well. If the problem persists, we will install the buffer tank recommended by Ecoforest to solve the problem, hoping that it will then resolve the issue. Considering the currently very small hot water tank (165 liters for 5 people), I would then opt for a combination tank ("with fresh water station") that has an internal hot water coil (no risk of legionella!).
I will report on Monday or Tuesday how it went.