So you have 170m² of heated area with screed.
If you assume 100kg/m², that is 17t of "buffer mass".
If you now add 500l, that is about 3% more.
I am familiar with the considerations of operating heat pumps in single-family houses without a buffer tank. The buffer tank costs some efficiency. Nonetheless, a buffer tank makes the overall heating system more "robust".
The calculation in the quote can be done that way, but the consideration and conclusion are not 100% correct. For one, it does not take into account that water mixes with water inside the buffer tank, i.e., heat transfer inside the buffer tank occurs significantly faster than heat release from the water through the outer walls of the heating coils into the screed.
Especially in autumn and spring, a buffer tank can help reduce frequent cycling of the heat pump.
As an example: roughly, the heat pump can "charge" about 11.5kWh into a 1000L buffer tank when it heats the storage from 35 to 45 degrees. By comparison: on a day in February, many rooms in the house may hardly "consume" heat due to solar gains — in that case without a buffer, the heat pump will run for much shorter times and tend to cycle more frequently.
If the house has photovoltaics or a variable electricity provider like Tibber is used, it can be interesting overall to charge the buffer tank during the day or at low-price times.
Since apparently very frequent cycling occurs in the current system, a buffer tank could at least help with cycling, possibly as a combined tank with a stainless steel coil in the buffer for hot water preparation in through-flow mode. But someone with expertise on site needs to examine this; remote diagnoses can be quite off.