Hello,
now I want to report how things turned out for us.
As written on 29.8., I have a single-family house from 53, with controlled residential ventilation and a room air-independent stove. The chimney sweep insisted on a pressure monitor or proof that no more than 8Pa negative pressure would occur in the house.

The proof was neither available from the manufacturer, nor from the planner or installer. They also suggest a pressure monitor.
The chimney sweep then reported the defect to the building authority.

In the end, we agreed with the chimney sweep on a pressure comparison measurement during regular operation.
The pressure difference was measured between outside air and the air in the stove installation room. That day it was quite windy and the pressure fluctuated by about 4Pa. No difference was detected whether the ventilation system was off, running at normal or full fan stage. With this, the chimney sweep’s conditions were met.
Additionally, I wanted a measurement with blocked supply air at full fan stage (worst case). Here the negative pressure in the room increased by about 2Pa, so a maximum of 5Pa was reached. Of course, one must say that although my house was extensively modernized, it does not reach the airtightness of a passive house.

Conclusion:
My RLU stove was approved without a pressure monitor.
The pressure test cost 250 euros.
For my safety, I hung up a CO alarm. It costs 50 euros, runs on battery, and must be completely replaced every 6 years. I claim it is safer and more reliable than a pressure monitor.

Regards
Michael
 

Vuffiraa

2014-11-14 15:12:31
  • #2


Hello Michael,

I would be interested in a few details about the pressure comparison measurement. Who carries it out? The measurement was certainly done before the installation of the stove? Was there an agreement with the chimney sweep up to what value he accepts the installation without a pressure monitor? I am thinking of a safety draft.

Best regards, Ulf
 

motte2

2014-11-14 18:33:23
  • #3
Hello Ulf, the pressure comparison measurement was carried out by a civil engineer who specializes in Blower Door tests. Local companies can easily be found on the internet. The measurement was conducted after the installation of the stove. The chimney sweep insisted that the stove be burning during the measurement. We conducted measurements before and after firing up and could not detect any difference. That is clear since the stove is room air-independent and we measured the pressure difference between indoor and outdoor air. The chimney sweep accepted a value up to 8Pa, which is the test pressure for RLU stoves. There was no mention of a safety exhaust; we did not even have to check failure scenarios such as fan failure, clogged filter, etc. Similarly, a stove door that is not properly closed or a defective seal is not taken into account. With a properly functioning controlled residential ventilation system, supply air and exhaust air are equal, so no pressure difference arises. Only when the supply air fails does a negative pressure build up. We simulated that. In our case, the negative pressure increased only slightly. I think in a passive house the 8Pa limit will then be exceeded. On the other hand, 8Pa can also be reached without a ventilation system just by the wind. Regards Michael
 

Vuffiraa

2014-11-18 12:44:09
  • #4
Thank you for the information.

The situation is somewhat different for us, as we live in a new building (Kfw70). The controlled residential ventilation also works with decentralized supply air (meaning holes in the walls) and a central fan for the exhaust air. Therefore, a slight negative pressure is created in our case due to the principle. However, the supply air valves cannot be hermetically sealed, so air can always flow in.

But I will discuss this with the chimney sweep...

Best regards Ulf
 

micric3

2019-09-11 07:02:32
  • #5


Hello Yvonne, did you have a controlled residential ventilation system installed?
 

ypg

2019-09-11 12:21:46
  • #6
Yes, certainly
 

Similar topics
01.03.2017Controlled residential ventilation - Yes or No?!31
25.08.2014Decentralized residential ventilation, exhaust air heat pump - experiences?10
17.12.2015What did you pay for your controlled residential ventilation system?16
26.04.2016Swedish stove or similar. With/without DIBt28
29.07.2017Install controlled residential ventilation yourself, stick to the schedule, costs?63
09.09.2016Controlled residential ventilation and disc valve - Passive House21
01.03.2017Controlled residential ventilation and extractor hood exhaust10
23.09.2016Which pressure switch should be provided for shutting down the controlled residential ventilation?25
09.09.2016Controlled residential ventilation and still open windows at night71
30.12.2016Geothermal heat pump with controlled living space ventilation or without18
27.01.2017Exhaust air vs. recirculated air in a controlled residential ventilation system32
15.10.2017Heating of the supply air in the pipe16
20.02.2018Is an oven and ventilation sensible?31
18.03.2024Attic problem. High humidity - Controlled residential ventilation?39
07.06.2018Controlled Residential Ventilation Single-Family House - Planning and Design Helios Easyplan34
18.03.2019Omit the single room rule? Controlled residential ventilation + gas heating, new construction57
01.04.2019Fireplace control / Pressure switch for shutdown Controlled residential ventilation16
15.06.2019KfW40 house offer with AWP and controlled residential ventilation, is it any good?39
27.02.2021Controlled residential ventilation + fireplace + kitchen exhaust, does it work?56
23.06.2021Controlled residential ventilation - Planning the positions for supply air / exhaust air60

Oben