These were initial experiments, the actual heating load is somewhere around 7kW.. I also have 230m² to heat.
The statement of the diagram is decisive for the calculation of the annual performance factor according to VDI 4650, because the bivalence point is important.
I just wanted to show THIS - how to determine the bivalence point.
According to the standard (and that is the only thing that matters for the subsidy), from the bivalence point -10° on, 100% compressor operation applies.
It makes no difference whether monoenergetic and bivalence point <= -10° or monovalent.
In reality, you will notice a difference. But not in the standardized calculation!
At -9°, I would no longer have reached the 4.5.
The statement of the diagram is decisive for the calculation of the annual performance factor according to VDI 4650, because the bivalence point is important.
I just wanted to show THIS - how to determine the bivalence point.
According to the standard (and that is the only thing that matters for the subsidy), from the bivalence point -10° on, 100% compressor operation applies.
It makes no difference whether monoenergetic and bivalence point <= -10° or monovalent.
In reality, you will notice a difference. But not in the standardized calculation!
At -9°, I would no longer have reached the 4.5.