Air heat pump B has the higher "own" performance at the design point (-14°C), yet has the worse annual performance factor in the yearly balance.
It is a fundamental mistake to design an air heat pump so that it delivers 100% heating capacity from its "own" power at the design point. Why? Heat generators are mostly operated in part-load range. The COP values determined on the manufacturers' test benches assume that the power produced is actually also used. This is quite legitimate, as they do not know every application case. The planner is responsible for this. He has to select the appropriate device based on the manufacturer’s characteristic curves (COP, heating capacity) that best fits the specific requirements.
What was done wrong in the past (undersizing, insufficient boundary conditions) is nowadays done incorrectly as well according to the motto "more is better," with similarly unpleasant consequences.
Well-planned air heat pump systems can achieve an annual performance factor of approx. 3.5 for heating and hot water, possibly slightly better. Poorly done systems are at 2.3..2.7, at best 3.0. What this means for the operator can be calculated by him with an expected service life of 20..25 years, provided the actual energy demand for heating and hot water is known.
Best regards.
How high the respective performance share of the air heat pump and possibly the heating rod is depends on the characteristic curve of the device in relation to the demand of the building....I wanted to explicitly point out that at -20° it probably heats purely electrically, so it is not a special achievement of the heat pump to get the house warm, .....
Air heat pump B has the higher "own" performance at the design point (-14°C), yet has the worse annual performance factor in the yearly balance.
It is a fundamental mistake to design an air heat pump so that it delivers 100% heating capacity from its "own" power at the design point. Why? Heat generators are mostly operated in part-load range. The COP values determined on the manufacturers' test benches assume that the power produced is actually also used. This is quite legitimate, as they do not know every application case. The planner is responsible for this. He has to select the appropriate device based on the manufacturer’s characteristic curves (COP, heating capacity) that best fits the specific requirements.
What was done wrong in the past (undersizing, insufficient boundary conditions) is nowadays done incorrectly as well according to the motto "more is better," with similarly unpleasant consequences.
Well-planned air heat pump systems can achieve an annual performance factor of approx. 3.5 for heating and hot water, possibly slightly better. Poorly done systems are at 2.3..2.7, at best 3.0. What this means for the operator can be calculated by him with an expected service life of 20..25 years, provided the actual energy demand for heating and hot water is known.
Best regards.