Bafa: Renewable Energy Heat Pumps with Test Certification

  • Erstellt am 2016-05-11 20:17:19

SirSydom

2016-06-15 12:53:12
  • #1
look at the Bafa list, the Cop value for A2W35 should be in the range > 4.2-4.3, then it is worth calculating.
 

Legurit

2016-06-15 13:56:42
  • #2
Do not undersize the heating system, otherwise it quickly becomes a bivalent operation and then the annual performance factor is ruined. We were almost desperate about that... V used an incorrect U-value (standard value for low energy and not ours) for our building envelope in the calculation and therefore ended up with too high a load - but this was later corrected.
 

Saruss

2016-06-15 14:00:44
  • #3


You can gladly enter that, but it also depends on what you actually achieve. Are your 30° flow temperatures really enough at -16°? (That must be very well insulated/tightly installed). Is the heating limit temperature really appropriate? How warm/cold is it really on average in your region during the heating season (location makes a big difference here!). How warm do you want your hot water to be (that can significantly lower the annual performance factor!).

In the actual tables from people who have an air-water heat pump, it often looks different.
 

SirSydom

2016-06-15 14:01:48
  • #4

One should know a heating load and then plot it into the performance diagram of the heating system. This way, the bivalence point can be calculated.

This is my heating system, the pink line is the heating load of 9.3 kW including hot water (at -16°).
With the "2er" heat pump, a bivalence point of -9° results, with the "3er" one of -13.2°.
 

SirSydom

2016-06-15 14:04:01
  • #5


30° flow temperature is contractually agreed for me.
Heating limit: no idea. I guess so.
How warm you want the hot water yourself has NOTHING to do with the "normalized" calculation of the annual performance factor according to VDI4650.

It’s not about consumption, but only about the subsidy.
 

Saruss

2016-06-15 15:56:12
  • #6


Well, the statement regarding the COP values (or the annual performance factor) is basically zero, because it does not say that the heat pump operates at -10° with a performance factor of 1.4 (or whatever). For that, you would need a corresponding additional diagram. Apart from that, the bivalence point does not have to be at the design temperature (that's what the heating rod is for, as is also the case with you); what matters is the region you build in – how often/long does it really get that cold in reality/statistics? You should not choose a "larger" heat pump just to save 5 operating hours of heating rod, since most of the time it runs at higher temperatures where excessive power is counterproductive. Your choice with the "2" looks okay, although the heating load of 9.3kW seems high to me. For me, my self-calculated heating load was lower than the "specified" one and has proven to be accurate in the last two years. Therefore, I see a certain risk of oversizing.

And indeed, when calculating a theoretical annual performance factor, the hot water behavior makes a difference!
 

Similar topics
29.11.2012Which heating system is currently the best?81
06.12.2015Heat pump / final energy demand / annual performance factor20
19.05.2016Gas or heat pump in a KfW55 house31
21.06.2016Heat pump with photovoltaics vs gas and solar thermal52
18.10.2016Which heat pump? Ventilation system / Air-to-water heat pump93
12.01.2019New construction - Energy consumption of the heat pump / electric auxiliary heater19
17.09.2020Alternative to Proxon air-to-air heat pump?28
22.11.2019Feedback on heat pump / offer requested!46
20.12.2019Difference in purchase cost between gas pump or heat pump74
07.05.2020Collaboration of air-water heat pump, photovoltaic system and storage38
24.01.2020Annual performance factor calculation for funding (parameters and calculation tool)29
05.02.2020LW Heat Pump Alpha Innotec LWDV with 12KW26
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
01.12.2020Eligible costs for heat pump134
08.12.2022Interpretation of iDM heat pump regarding COP32
02.03.2023Heat pump for KfW55 house 148 sqm99
02.10.2023Estimate electricity consumption with heat pump30
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16

Oben