Annual performance factor calculation for funding (parameters and calculation tool)

  • Erstellt am 2020-01-23 06:48:50

boxandroof

2020-01-23 19:41:04
  • #1
If the heating load is correct, a 12kW unit would be more sensible, especially if the lower modulation limit is reduced as a result. I was able to have my underfloor heating planned verifiably at 28/24 with -12° standard outdoor temperature.
 

freisinger

2020-01-23 20:24:24
  • #2
Regarding "room-by-room heating load calculation": no, it does not exist. Neither of the two heating installers does it without an advance payment. Regarding 12KW machine: I want to receive the subsidies. For this, an annual performance factor of 4.5 must be achieved with an air-to-water heat pump, or a soil-to-water or water-to-water heat pump must be used. We have a standard outside temperature of -13.7. So I don't find an air-to-water heat pump. Really a shame and annoying.
 

Daniel-Sp

2020-01-23 21:44:39
  • #3
How can the heating engineer make a statement about possible/impossible flow/return temperature without an existing room-specific heating load calculation? Considering the size of the house, I do not assume that it is built on a towel-sized plot. Is a ring trench collector not possible?
 

freisinger

2020-01-23 22:02:08
  • #4
The property around is somewhat smaller due to the size of the house. We have a garden of about 240 sqm in front of us. But with a brine heat pump, the storage tank must fit the 10,000 houses subsidy. Which the heating installer does not have. Now I have found a Nibe 2120-12. At -14 degrees and a flow/return temperature of 35/27, it would achieve an annual performance factor of exactly 4.5. Is the flow/return temperature valid?
 

Daniel-Sp

2020-01-23 22:16:30
  • #5
What kind of storage is then required? DHW or heating buffer tank?
 

Daniel-Sp

2020-01-23 22:34:45
  • #6
35/27 should be possible, but it does not exempt you and your planner from a calculation tailored to your object. Otherwise, it will go wrong despite obtained funding. Estimates, assumptions, gut feeling, and rough approximations often lead to problems with heat pumps, as can be read here and elsewhere repeatedly.
 

Similar topics
19.05.2021Experiences with brine heat pump491
06.12.2015Heat pump / final energy demand / annual performance factor20
07.10.2016BAFA funding tips38
10.10.2017New photovoltaic system with storage in single-family house - experiences39
30.09.2018BAFA funding for air-water heat pumps in new construction - how does it work?30
22.02.2018Air-water heat pump, water-based pellet stove, and photovoltaic system17
07.05.2020Collaboration of air-water heat pump, photovoltaic system and storage38
20.01.2020New BAFA funding - Air-to-water heat pump with solar thermal39
25.10.2020KfW 55 or 40+ for new single-family house construction in Würzburg?27
14.10.2022Air-to-water heat pump sizing in new construction311
14.02.2024Bafa funding for heat pumps will be discontinued as of 31.12.2020.510
21.01.2022Is it still possible to apply for KfW55 funding?24
14.06.2022KfW BEG funding stopped 261, 262, 263, 264, 461, 463, 4641239
10.04.2022Construction project on hold - keep the property or sell it?25
13.04.2022Start a construction project, buy only the land or wait?30
04.08.2022Buy an existing single-family house with a large plot and renovate it22
07.01.2024KfW Funding Climate-Friendly Residential Building from March 2023152
07.03.2024New funding for family home ownership201
18.03.2024Buy the land first and then finance it?29
16.08.2024Buy land with cash, construction through KfW/NRW Bank27

Oben