And if you close them via KNX, does the flow indicator also change (to zero)?
Or does it stay there?
Goes to 0
I suspect you don’t mean SMT but MDT?
Exactly that gauge I have installed myself.
Some of them need a 1-degree correction!
So measure again with a precise thermometer.
Yes sorry, I meant MDT. As I said, we all even checked with a calibrated thermometer. I had borrowed it from work.
Rooms showing 21.5 degrees also feel comfortable, the one room with 19.9 is noticeably colder when entering. From the “feeling” the switching of the actuators corresponds to the measured temperature. As said, the measurement showed no anomalies here.
You won’t have any chance with an expert if you don’t increase the supply temperature and show that it still won’t get warm...
You’re probably right, that was more of an emotional reaction on my part out of desperation.
Basically, I have the feeling you’re looking here for the one, all-solving answer.
But a hydraulic balancing is tedious work over several weeks.
So proceed as follows:
- Calibrate all thermometers or use exact external ones
- Ensure that the Taco setter valves show correctly
- Disconnect KNX control or permanently switch all actuators on
- then start throttling the too warm room a bit
- continue this until the temperatures are right everywhere.
What’s already noticeable is that the smaller purple room has more flow than the significantly larger red one.
That can’t be right
Yes, I had hoped to have overlooked something in the matrix but apparently that’s not the case.
I can’t do the hydraulic balancing again at the moment...
Shortly after the heating season started, I set everything to manual at full flow. Waited two days. Noticed all rooms warmed up except “red”. Then started throttling the first room. That took another three days. Then the second room, which was okay after the first adjustment, and so on. That cost me over two weeks and almost drove me crazy. After that came thermal imaging camera, flow tester and we even adjusted the ventilation system up and down...
The result was: all rooms as I want them, except that one room just wouldn’t get warm.
We also checked the insulation in the cold attic above the concrete ceiling for gaps.
Honestly, I don’t know what hydraulic balancing is supposed to bring in this case? The fact that heat energy doesn’t get into the room is contradicted by the visibly fully open valves. About 3L/min arrive at both valves. You can read that off. The flow corresponds to that of the neighboring room. Heating circuit lengths and number are identical. So where does the 1.5-degree difference come from? I can’t reconcile that with a possibly missing hydraulic balancing.
To produce a 1.5-degree difference in room temperature under the same conditions, the flow would have to be 20-30% lower, which you would immediately see.
I’m now setting the valves to manual and 100% again and raising the supply temperature to 29 degrees to see what happens to that room; I can’t think of anything better right now.