TGA planner, but that costs money. Otherwise, read up on the knowledge yourself (specialist forums on building services engineering, there have been some good posts in this forum for some time) and work together with good craftsmen. They can definitely do it if you give them a few specifications.

Plan the underfloor heating with a maximum flow temperature of 30-32° based on room-by-room heat load calculation. All circuits about 80 meters, maximum 100. Avoid very small circuits. If you manage this early on, you are on a good path.

Heat pump without buffer storage.
 

ludwig88sta

2019-12-17 19:02:57
  • #2
Thank you. But I am surprised that the heating engineer does not know these "standards"? They also want to have a good reputation, so that customers are satisfied afterwards and recommend them. He must be proficient in the subject.
 

boxandroof

2019-12-17 19:12:12
  • #3
The heating engineers are often commissioned by the main contractors, where reputation counts little, but it must be cheap. Quick estimates and few meters of pipe.

The heating engineer I commissioned was very competent, I presented him with plans and was able to discuss them well with him. However, I do not know how he would have planned for me on his own initiative.

And if the manufacturer states that a buffer tank is mandatory, then the heating engineer will install it that way. Unless you explicitly commission it differently.

What is of no use during construction is to be surprised about anything.
 

ludwig88sta

2019-12-17 19:24:09
  • #4


A buffer tank only makes sense with a normal heating system, but not with pure underfloor heating. Well, the general contractor basically wants to sell their contractual equipment and the unaware homeowner / buyer still ends up with the buffer tank....
I understand
 

boxandroof

2019-12-17 19:43:36
  • #5
The manufacturers of heat pumps partially require it. It is also somewhat understandable because individual room control is mandatory ([Energy Saving Ordinance]).

Heat pumps require flow, which is not compatible with individual room control. If all thermostats are closed, then the heat pump can charge the buffer. An alternative to the buffer are bypass valves, which should also be avoided or closed when the [ERR] is removed. It is also easier for the heating installer: with an overly warm buffer storage and individual room control, the occupants can just adjust the thermostats as usual. It gets warm and everyone is happy for the time being.
 

Wickie

2019-12-18 06:46:28
  • #6
The Heizis are familiar with gas because it has been a well-known technology for decades. However, if someone now tries to simply replace heat source 1 (Gas) with heat source 2 (Wärmepumpe), the whole drama begins. That was our feeling!
 

Similar topics
21.12.2015The matter with heating - air/air, air/water, or gas?28
19.03.2016Underfloor heating vs. flat radiators14
15.03.2017Expert assessment for underfloor heating in a single-family house10
06.09.2018Annual consumption of air-to-water heat pump plausible?10
10.04.2019LWZ 504 with or without buffer tank14
07.01.2019Is gas condensing boiler heating sensible for a newly built single-family house according to the Energy Saving Ordinance 2016?28
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
04.02.2020Whom to entrust with the room-wise heating load calculation?46
24.02.2020Freshwater station and buffer tank: technically better choice?24
01.03.2020Protective pipe for underfloor heating forgotten in the area of movement joints39
03.01.2022Geothermal heat pump single-family house 200m² underfloor heating kfw55 - setting/optimization91
08.02.2022How complicated are heat pumps in practical operation?78
26.04.2022Air-to-water heat pump without buffer storage | Heating installer refers to building energy law requirement33
31.03.2022Air-Water Heat Pump - Buffer Storage Yes or No?28
19.04.2022Smart home for underfloor heating in a KfW40+ house?30
25.04.2022Heating Concept Air-Water Heat Pump Single-Family House 2 Persons - Offer from Heating Technician?15
08.06.2022Distance of buffer tank to ground source heat pump19
18.11.2022Save gas or shop cheaply?19
24.11.2023Heat pump: buffer tank, capacity and modulation46

Oben