That would basically be the compressor hysteresis for me, which I think I can set from 3k to a max of 15k; however, the compressor is then locked, and I have no influence on this lockout time.
Normally, the system regulates via the energy integral, which is fixed at -180 degree-minutes.
For every minute that the flow temperature (thanks to the compressor hysteresis) is above the flow setpoint temperature, the -180 moves towards 0. Accordingly, at 0, the compressor would switch off until the switched-on value (compressor start currently at -120) is reached. Unless the flow reaches the set max hysteresis before the energy integral is depleted; in that case, the compressor would be locked accordingly. Sounds kind of confusing, but I can't explain it any better.
So in summary
If the flow actual is above the flow setpoint, the 180-minute counter counts down to 0 (unless the compressor hysteresis intervenes earlier). If the flow actual is below the flow setpoint, it counts from 0 back up to 180, whereby the compressor switches on again at 120 and starts heating until the flow actual is above the flow setpoint again, and the cycle starts over.